Discuss Full rewire needed? First time home owner in the UK Electrical Forum area at ElectriciansForums.net

Figment ov your imagination.
Nonsense. And what's this then?

CU.png
 
@Pretty Mouth
I had the same question... It's why I thought he had only one RCD... In fact, this is probably a bug on the picture.

And I didn't see the 1 to 4 circuit breakers where RCBO...
So, the wiring seems to be ok. But there are probably only a few sockets per room.

For information, I will have at least 6 sockets per bedroom and 12 in the kitchen. We never have enough sockets... An upgrade is probably the best option.
 
Last edited:
You've got an installation that is approaching, if not reached, the end of its design life.

That is not to say it won't soldier on fault free for another ten years but you have to ask, are you feeling lucky?

Now is the time to do this before you go mad with the Farrow&Ball and Italian tiles.

Its the one thing stopping me from moving. We both want an older property but there's no way I could start decorating without rewiring. When we look at houses the better half looks how immaculate it is, I'm thinking how much I'd have to rip apart.

Best of luck with the house.
 
Its the one thing stopping me from moving. We both want an older property but there's no way I could start decorating without rewiring. When we look at houses the better half looks how immaculate it is, I'm thinking how much I'd have to rip apart.

I grew up in an old house and still feel like I'm painting the Forth Bridge in trying to maintain it for my folks. If I was in the shoes my parents wore when they bought that place, (and knowing what I know now) I'd have endured many hardships to ensure the infrastructure was as sounds as could be, before any decorative works took place.
 
@Matthewd29
I just checked my wiring diagram. In fact, it will be only 32 circuit breakers... I've got electric heaters, with a circuit breaker for each one (not compulsory), and a lot of specific circuits with 1 circuit breaker for each one (compulsory) : fridge, oven, washing machine, ...
And also, there will be a big communication panel (TV, ethernet,...). This will be a huge wiring for a small flat.
As this flat will be considered as a new flat (I have no electricity at the moment), I need to respect the rules to pass the control. And in France, it's compulsory and very strict !

32 circuit breakers in a 2 bed flat is frankly ridiculous. Do the French regs really demand this?
 
The minimum necessary is probably around 15 breakers (this is a flat with electric radiators). But it means you would have only 2 or 3 outlets per room, only one light point per room...

Number of breakers necessary for each circuit :
1 - roller blinds
1 - Mechanical ventilation
1 - washing machine
1 - tumble dryer
1 - dishwasher
1 - oven
1 - electric hob
1 - freezer
1 - water heater
1 - day/night water heater management protection
2 - outlets (around 23 outlets compulsory for such a flat) - maxi 12 outlets per breaker (2,5 mm2 wire, 20A breaker)
2 - electric radiators (5 radiators)
1 - light (max 8 light points per circuit breaker)
Total: 15

But I increased the number of breakers for this :
  • 3 for electric radiators (1 circuit breaker per radiator)
  • 1 for heating manager
  • 3 for lights : 1 circuit breaker for 2 rooms (many light points per room)
  • 5 for outlets : 1 circuit breaker per room and even 2 for the kitchen and 2 for the living room
  • 1 for extractor hood
  • 1 for door bell
  • 1 for balcony light and outlets
  • 1 for communication panel outlets,...
 
@Pretty Mouth
I had the same question... It's why I thought he had only one RCD... In fact, this is probably a bug on the picture.

And I didn't see the 1 to 4 circuit breakers where RCBO...
So, the wiring seems to be ok. But there are probably only a few sockets per room.

For information, I will have at least 6 sockets per bedroom and 12 in the kitchen. We never have enough sockets... An upgrade is probably the best option.
I hope the 12 sockets in the kitchen are on two separate radials only 6 allowed on any one circuit in the kitchen in France.
 
The minimum necessary is probably around 15 breakers (this is a flat with electric radiators). But it means you would have only 2 or 3 outlets per room, only one light point per room...

Number of breakers necessary for each circuit :
1 - roller blinds
1 - Mechanical ventilation
1 - washing machine
1 - tumble dryer
1 - dishwasher
1 - oven
1 - electric hob
1 - freezer
1 - water heater
1 - day/night water heater management protection
2 - outlets (around 23 outlets compulsory for such a flat) - maxi 12 outlets per breaker (2,5 mm2 wire, 20A breaker)
2 - electric radiators (5 radiators)
1 - light (max 8 light points per circuit breaker)
Total: 15

But I increased the number of breakers for this :
  • 3 for electric radiators (1 circuit breaker per radiator)
  • 1 for heating manager
  • 3 for lights : 1 circuit breaker for 2 rooms (many light points per room)
  • 5 for outlets : 1 circuit breaker per room and even 2 for the kitchen and 2 for the living room
  • 1 for extractor hood
  • 1 for door bell
  • 1 for balcony light and outlets
  • 1 for communication panel outlets,...
I would also suggest a separate breaker for:
Smoke alarm
Burglar alarm.

telerupteurs? Suggest electronic rather than the mechanical latching relay which would be very noisy in a small flat, probably four or five needed and they are additional to those listed, but admit have gone over to Quintonic in the last year or so, saves chasing the walls out for switch points when adding a circuit. (old stone property)

That makes 34 breakers which will require five RCD's, (DD's in France) taking into account the requirement of only eight breakers off any DD, that's a minimum of a four row board without any room for expansion, puts my four row board in the shadeDSC00487.jpeg
 
Last edited:
From rewire advice to circuit protection Top Trumps.

I'm curious about this French flat and whether or not it has a dedicated plant room to house all of these protective devices? Does it utilise RCBOs or are several circuits liable to be taken out by a single RCCB?

I'm sure the OP is delighted to know that continental conventions lavishly throw circuit protection at installations as though they were confetti, but perhaps it might be an idea to explain why this would be better? British convention allows protection of a 2 bed flat from a distribution board no bigger than a box of chocolates, populated by by protective devices that break both poles and provide earth leakage protection to individual circuits. What's better about a board that's as big as a Chevrolet?
 

Reply to Full rewire needed? First time home owner in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
856
Hi all, I posted here some time ago asking for validation of a quote I received for a rewire. (10k assumed 60 points) And got some good advice so...
Replies
2
Views
590
Hello. Homeowner trying to understand what is a fair quote for full rewire. We've had to tear the ceilings down as part of unplanned asbestos...
Replies
8
Views
2K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
746

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock