happy Monday evening chaps!

haven't got my regs handy so for quoting purpose I tried using the tlc calculator but it says 'no suitable cable found'

run is apparently 100m -going my customers email -quoting on thurs
load is: (as per customer)
PC with 4 screens
Sonos One speaker
2 x LED ceiling lights
1 x LED security light
1 x Gree home air conditioner/dehumidifier/heater 5Kw
1 x Kettle

swa to be cleated rather than buried

so using Voltage Drop Calculator | TLC Electrical - https://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
I allowed for 8kw- with lighting circuit @ 100m and says 'no suitable cable found'

obviously will check my book when I can but if any of you have any quick comebacks

would have thought 10mm 3core at 100m may be a push!
so poss 16mm

not sure if tns or tncs yet- will find out thurs
 
If you want to keep below the 3% VD for lighting, you'll have to go up to 25mm².
 
happy Monday evening chaps!

haven't got my regs handy so for quoting purpose I tried using the tlc calculator but it says 'no suitable cable found'

run is apparently 100m -going my customers email -quoting on thurs
load is: (as per customer)
PC with 4 screens
Sonos One speaker
2 x LED ceiling lights
1 x LED security light
1 x Gree home air conditioner/dehumidifier/heater 5Kw
1 x Kettle

swa to be cleated rather than buried

so using Voltage Drop Calculator | TLC Electrical - https://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
I allowed for 8kw- with lighting circuit @ 100m and says 'no suitable cable found'

obviously will check my book when I can but if any of you have any quick comebacks

would have thought 10mm 3core at 100m may be a push!
so poss 16mm

not sure if tns or tncs yet- will find out thurs

3%.PNG


5%.PNG


disconnection.PNG
 
What software is that lee?
 
Plus, of course, the cable will only be running at a small proportion of its rated current, so its temperature will be below rated, so the conductor resistance and therefore volt drop will be lower than shown by the usual simple calc.
 
  • Like
Reactions: Leesparkykent
Hi - that is spooky cool Lee. Looking at it, it seems to show that if it's TNS up near the top end then 40A MCB may have to be derated? (run it again run it again :) )
 
  • Like
Reactions: Leesparkykent
Lee

Do you rate this software - been thinking about buying something for a while now and at £19.99 it seems OK!

Your thoughts?


Thanks
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

J.C.E

Arms
~
Joined
Location
Earth

Thread Information

Title
garden office supply
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
J.C.E,
Last reply from
Octopus,
Replies
15
Views
152

Advert