Hi there.
I want power in my garage which is NOT attached to my house, its around 20-25 meters from the main house consumer unit to the garage.
There is conduit installed underground going from the House consumer unit, to the garage.
Also in my main Consumer unit I have a 32amp spare breaker for the garage.
Am I right in thinking I can use 6mm SWA going from the 32amp breaker, under ground and up into a mini consumer 2 breaker unit in the garage?
All there will be in the garage is a few plug sockets and a couple of strip lights.
Any help will be appreciated.
Thanks!