Discuss high current in main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
56
Hi
i'm testing a very large office complex. at the source, a 800A busbar system, i put my clamp on the main earth and found 7A. Would this be due to the high number of computers used throughout the building, and is the 7a dangerous/not compliant with the regs.

also i put my clamp around a couple of SWAs and found 3A, i'm surprised as i thought the currents in the live and neutral would balance each other out. can anyone explain this.
note: the installation is the old MEM Exel stuff and is 40 years old.

thanks
 
Ive had similar currents in main earthing conductors on office blocks, it common with large no' of computors, electronic lighting ballasts, patch panel systems etc its a functional earth and all the mA leakage adds up.
 
L&N will cancel each other so you’re measuring the leakage. With an 800A supply I wouldn’t worry about 7A. It’s probably higher, the average clamp meter doesn’t cope with harmonics very well. Is you’re meter calibrated by the way?
 
I also wouldn't worry about 7 Amps leakage current on a 800A office complex supply as long as there's no elevated voltage developing on the N or E.
 
Last edited:

Reply to high current in main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
A bit of a mini essay but these questions have been building up in my mind over the last weeks and months as I've been studying and volunteering...
Replies
6
Views
3K
Hi All Sorry for the lengthy first post and use of any non-standard terminology. I'm a bit of a novice when it comes to electronics, hopefully...
Replies
88
Views
19K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock