Hello all,

This is my first thread as joining the group to hopefully learn and possibly assist. I have been a industral engineer for many moons and started as a sprky with a 4 year apprenticeship (yes a long time ago!) - back in those days testing seemed easier and less complex than today but that may be age again! Anyway, I decided to upgrade my old testers for a new Ideal Suretest and it seems ideal for the likes of me, but whilst playing at home on the ZE (P-E) i was getting high readings which also tripped the 63amp 30ma RCCB on a crabtree board, the L-N reading was good but when i carried a ramp test the RCD was tripping early. would this impact on the ZE regarding i was getting or could this be a seperate problem?

always keen to hear advice!

Ben
 
need to see actual readings, saying it's high or it trips too early isn't enough for us here.
 
first, were you testing Ze at the main sitch with the installation OFF and the earthing dissed? or were you doing Zs . if the latter, were you using no-trip? also RCDs will usually trip around 23mA. this is bordering on the safe side so as to ensure tripping at 30mA.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High ZE readings
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Thread Tags

Tags Tags
readings

Advert

Thread statistics

Created
ben1973,
Last reply from
telectrix,
Replies
2
Views
1,337

Advert