Ahh the freezer, at least you know what it is!!
What you pretty much found but couldn't confirm first time.
What you pretty much found but couldn't confirm first time.
Discuss Kitchen Ring earth fault? in the Australia area at ElectriciansForums.net
the other thing to note is the MWC itself asks for "details of the modified circuit". replacing a fitting /accessory is not modifying the circuit. therefore, IMO, no certificate is required (although i do not dispute the idea that it may be advantageous to complete a test of the circuit and issue a MW
edit:sorry, double post.
Thanks to most of you guys for all your responses apart from the odd 1 or 2 of you. If you got nothing helpful to say, I`d rather you not comment on my threads.
I was back on the job today with my tester, I done ring end to end continuity 0.51 L-L 0.52 N-N 0.84 E-E. IR test, lowest reading i got was 250M Ohm.
Everything in the house stays on, under load aswell untill I plug the freezer in and.....boom RCD trips within 30secs. So my conclusion is the freezer is the problem ( its a smeg under counter job if that helps ) Ive never claimed to be an 20 - 40 year experienced spark, thats why I am on this forum which I find a great source of info from lots of experienced sparks.
Im new to testing and fault finding so am I missing something Guys?