Had an old Fluke for years, which has incidentally been faultless . Company purchased a Megger last year however when doing Internal earth fault loop impedance readings are far higher than expected.

I.e..example

Ze = 0.20ohms
r1 + r2 = 0.15ohms
Zs should be about 0.35ohms however coming back around an 1ohm so obviously not right.

Anyway, after a bit of fiddling established it was the Rcd causing the drastic increase in resistance. However my old fluke does't suffer from this problem. So Megger was sent back for repair and no problem found??

Anyway, a Seaward tester turned up in the stores this week and tried that. Same bloody problem!! Likewise that will be going back.

Am I doing something wrong?? Stick with the old fluke I think!!

Any thoughts? TIA

Edit: I'm sorry I don't know the model numbers off hand
 
Think your find its to do with 3 wire low current testing. Someone more clever than me will explain it to you. Apparently Megger MFT's are prone to it, although I've not experienced it with mine. You could try 2 wire test, isolating the RCD to verify. Think davesparks uses that test all the time, hopefully he'll be along soon to explain.
 
Basic explanation - the Flukes send very short bursts of high current down the lines, then calculate the result, the other Makes send low current, longer duration bursts down the lines to then claculate the result.

This gives more variation in the result between different makes, as using a low current cannot accurately measure the earth loop.
Try it on a non-rcd protected source on both high and low current tests, and the results will very likely not be the same from the same tester.
 
Basic explanation - the Flukes send very short bursts of high current down the lines, then calculate the result, the other Makes send low current, longer duration bursts down the lines to then claculate the result.

This gives more variation in the result between different makes, as using a low current cannot accurately measure the earth loop.
Try it on a non-rcd protected source on both high and low current tests, and the results will very likely not be the same from the same tester.

Thank you for your reply.

Am I right in thinking the high current test trips RCD's? If this is the case, then to get any kind of accurate reading i'm going to have to bypass the RCD each and every time?! :freak:

Not going to happen! Most times, assuming the circuit is good, my colleague and I can basically guess what the Zs will be using the Fluke by judging the run. This gives us confidence when you get a result that it's correct or not.

Sticking with my old tester I think!!
 
there is a way to avoid bypassing the RCD with links. turn MCB off and lock off. link L-E at the furthest point on the circuit, then measure Zs at the CU. sintra has a step by step guide for this.
 
I drew this diagram to show the above, there are many points within the CU that you can test, just make sure that the circuit you are testing is isolated and remember to remove the remote line earth link!! Top one is normal, bottom one is avoiding tripping the RCD.
Alternative Zs bypassing RCD.jpg
 

Reply to Loop tests and RCD's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, installed some circuits in a factory. The circuits were tapped off of a busbar that goes straight to the main switchgear. From this I...
Replies
3
Views
2K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K
I forgot I had a Di-Log 9803P so called '17th Edition Tester!?', it was a rash ebay purchase a long while ago intended as a spare, and I discarded...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock