Richard
Had an old Fluke for years, which has incidentally been faultless . Company purchased a Megger last year however when doing Internal earth fault loop impedance readings are far higher than expected.
I.e..example
Ze = 0.20ohms
r1 + r2 = 0.15ohms
Zs should be about 0.35ohms however coming back around an 1ohm so obviously not right.
Anyway, after a bit of fiddling established it was the Rcd causing the drastic increase in resistance. However my old fluke does't suffer from this problem. So Megger was sent back for repair and no problem found??
Anyway, a Seaward tester turned up in the stores this week and tried that. Same bloody problem!! Likewise that will be going back.
Am I doing something wrong?? Stick with the old fluke I think!!
Any thoughts? TIA
Edit: I'm sorry I don't know the model numbers off hand
I.e..example
Ze = 0.20ohms
r1 + r2 = 0.15ohms
Zs should be about 0.35ohms however coming back around an 1ohm so obviously not right.
Anyway, after a bit of fiddling established it was the Rcd causing the drastic increase in resistance. However my old fluke does't suffer from this problem. So Megger was sent back for repair and no problem found??
Anyway, a Seaward tester turned up in the stores this week and tried that. Same bloody problem!! Likewise that will be going back.
Am I doing something wrong?? Stick with the old fluke I think!!
Any thoughts? TIA
Edit: I'm sorry I don't know the model numbers off hand