Discuss Main Feed for 3 phase unit. What size cable would be best? in the Electrical Forum Canada area at ElectriciansForums.net
M
mgnelec09
I went looking at a job yesterday.
It is going to be a commercial office block with 3 large offices with around 25 d/sockets in each.
There is a large sub main in an adjacent building about 40 metres away.
It is all going to separately metered .
I am just aking your opinions on what size supply cable would be suitable to run from the sub main to the building which will be supplying 3 x 100amp single phase consumer units.
any suggestions?
25mm will give you 100A/phase. whether you want to go larger to allow for increase in demand is your call. have to do a volt drop calc. should be OK at 40m.
top of me 'ed abvout 8volts at 100A,40m.
do your vd calc. at 100A , 40m. my figure of 8v is a guesstimate.
Reply to Main Feed for 3 phase unit. What size cable would be best? in the Electrical Forum Canada area at ElectriciansForums.net
Hi, we are converting old farm buildings to commercial units, and as my father used to run a vacuum pump and compressor in his dairy I always...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
