Tasked with changing all the lights in the communal areas of a block of flats.
At the moment all fittings are thorn 28W 2D with emergency back up that are permanently on.
Client has specified Lumineaux 16W 2 D bulkhead emergency/sensor fittings.
This would mean that the fittings above the fire doors to the stairwell and the stairwell itself would not be a maintained fitting, rather they would be on a movement sensor.
I seem to recall that lights in these locations would have to be maintained, but I'm not back in the office to be able to check for a few days, probably monday.
Useful answers please. Random insults accepted if they are funny.
 
  • Like
Reactions: 2 people
tazz is your expert here, but i would imagine that they should be maintained.
 
They need to be maintained...but this is not a problem, as the lightings your fitting in the communial areas are themselves maintained. All with have a permanent Line and neutral, At the exit lights, bridge the switch and permanent line together, most units have a link wire just for this situation.
 
They need to be maintained...but this is not a problem, as the lightings your fitting in the communial areas are themselves maintained. All with have a permanent Line and neutral, At the exit lights, bridge the switch and permanent line together, most units have a link wire just for this situation.

Thank you for the conformation, I had that suspicion. Yes, no problem linking these fittings out to make them maintained.

One other question, on the stair well there is a light at every landing and half landing, I'm sure not all these need to be maintained, just the one by the final exit door.
I'm looking at you Tazz :)
 
The staircases can be used with pir sensors, but make sure they are set with more than enough time to walk up or down. And they work correctly, otherwise it becomes a dangerous situation with no lighting.
 
Tazz - should here be a design carried out first? My understanding is that the design should be signed off also. Even more so in a multi occapancy building like this?
 
If it was a new build it would, the op`s job is for replacement units, so old design stands, but will need checking. Modification/or install cert with final commissioning and handover certs will be required
 
  • Like
Reactions: 2 people
The staircases can be used with pir sensors, but make sure they are set with more than enough time to walk up or down. And they work correctly, otherwise it becomes a dangerous situation with no lighting.

Apparently each unit has its own built in PIR - never used them before, as I said specced by the management company who look after lots of properties all along the south coast.
 

Nope, no humming or buzzing, work quietly.
I like the dip switch settings for sensitivity, lux and time, neat fitting.
Although the cable entry is near the edge of the fitting, and all the existing ones were in the middle, new hole and cable fishing ensued, fortunately the original installers left plenty of slack.
Out of laziness can anyone quote me the building reg location for maintained fittings by exit doors, save me hunting for it on monday, apparently we are the only electricians to of mentioned it and the estate management people would like it as a reference.
 
Just went hmmm so could locate thread again as I'm doing 3 story Hmo soon and these lights might be the ones for the stairwells and exits.
 
Instead of sensor and pendant with 8w bulk head mounted beside them
 
Nope, no humming or buzzing, work quietly.
I like the dip switch settings for sensitivity, lux and time, neat fitting.
Although the cable entry is near the edge of the fitting, and all the existing ones were in the middle, new hole and cable fishing ensued, fortunately the original installers left plenty of slack.
Out of laziness can anyone quote me the building reg location for maintained fittings by exit doors, save me hunting for it on monday, apparently we are the only electricians to of mentioned it and the estate management people would like it as a reference.

Is there a building regulation with regards to location of fittings ?

May be wrong, but I thought you had to work to BS 5226-1 ?




 
Is there a building regulation with regards to location of fittings ?

May be wrong, but I thought you had to work to BS 5226-1 ?






My understanding is that non-maintained fittings would be used in a building where the users would be familier with the building. Maintained fittings would be fitted where users are not familier. Such as a block of flats or a cinema.

Fittings should light up fire extinguisers, fire blankets, first aid kits, call points, communual areas - change of direction/level, steps and at the final exit of buildings, both internal and external.

There are bound to be more but have a look at the electricians guide to emergency lighting.
 
All em lighting comes under BS5266....There is no rule for using maintained lighting in public buildings, But most designers will used maintained because the look better then a load of cheap non maintained bulkheads fittings, screwed to a ceiling next to an expensive fitting.
The use of a maintained fittings, allows all the lighting in a corridor, to look neat and match normal fittings, and to used as such. The result looks better and sensors or normal switching can be used.

This is a nursing home, we ripped all lighting out, and replace with led sensor fitting...every 3rd light fitting is a maintained em light....you must agree it looks neater when all lighting is the same

2013-09-17 19.22.35.jpg
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Doomed

Arms
~
Joined
Location
Dorset

Thread Information

Title
Maintained or not?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Doomed,
Last reply from
tazz,
Replies
17
Views
2,156

Advert