Chector

Hi, I've changed a consumer unit for a customer but noticed the earth and bonding conductors were undersized at 6mm csa. Do I put this down as a departure from 7671 or not issue to cert until the problem is rectified?

Thanks

Chris
 
Perhaps it would have been best to have tested and replaced if necessary before you changed the CU. that would have been my choice, others may differ though.
 
dont do much domestic but would imagine you can still certify the work you have completed and code the bonding accordingly but also stress the importance of the rectification works to the customer.
 
Hello,

Please do not take this the wrong way, but having looked at your profile you say you are an electrician and not a trainee, so can only give you advise based on this level of standing.

When you carried out all your pre checks and tests on the old consumer unit / fuse box, you would have noticed that the main protective bonding conductors were less that the size they should ideally be.

What size is the main fuse, and what size are the meter tails please.

On the basis the tails are >16mm then I would want to see 10mm bonding conductors to the main services, be it water or gas etc.

Any electrical work that you undertake, the earthing must be up to standard, in my opinion putting it down as a departure on the certificate is not the correct way of doing it as they are there to help save your life, so on that basis, making a note on the cert is not right.

You should have updated the earthing and bonding arrangements prior to your changing the consumer unit or at the same time as, because now, you have energized an installation that is potentially unsafe, ok no worse than it was before, but thats not the point.

Some will say if theres no signs of thermal damage etc to the bonding conductors and the BS951 clamps are in good order with sound connections, but if it was me I would want a 16mm main earthing conductor, and 10mm main protective bonding conductors.

What color is the 6mm you have got, is it green and yellow or solid green?

Also, what size is the earthing conductor and what supply type is it? TNS? TNC-S? TT?
 
With reference to a post you made just 5 days ago, I can only assume this is the same property:

"I would value peoples opinions the earthing arrangement I cam across yesterday. Water and Gas main protective bonding conductors were not installed at the consumer unit, but were coned to the main earthing terminal. The MET was connected to the distributors earth and one conductor ran from the MET to the consumer unit. The resistance from the consumer unit to the gas and water were fine at 0.01 Ohms. But shouldn't the conductors be wired into the consumer unit? They all need changing anyway as they were all 6mm."

http://www.electriciansforums.co.uk...trical-forum/102345-earthing-arrangement.html

So based on this, you knew they were on the small side before you started the work, so why have you carried on and not updated them?
 
as trhe previous post #6. 10mm main bonding is only required on a PME system, and even then can be left as is if certain conditions are met.
 
Hi, I've changed a consumer unit for a customer but noticed the earth and bonding conductors were undersized at 6mm csa. Do I put this down as a departure from 7671 or not issue to cert until the problem is rectified?

Thanks

Chris

"No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate."

If you have confirmed that the earthing and bonding arangements are adequate then issue your cert. If not then as you have carried out work then it is up to you to make them adequate.

 
"No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, shall be adequate."

If you have confirmed that the earthing and bonding arangements are adequate then issue your cert. If not then as you have carried out work then it is up to you to make them adequate.


Hey S, your quote reads as authoritative, please would you quote its source in order to confirm its authority beyond being 'sensible practice' and good advice from an experienced electrician and a moderator or administrator on this site?
 
Hey S, your quote reads as authoritative, please would you quote its source in order to confirm its authority beyond being 'sensible practice' and good advice from an experienced electrician and a moderator or administrator on this site?

I take it you are asking this for the benefit of the OP ? Even though he really should know where this is from being a practising electrician. Not sure it matters anyway as he seems to have cleared off like his last thread.

BS7671, chapter 13 fundamental principles, regulation 132.16 to save Sintra a job.
 
I take it you are asking this for the benefit of the OP ? Even though he really should know where this is from being a practising electrician. Not sure it matters anyway as he seems to have cleared off like his last thread.

BS7671, chapter 13 fundamental principles, regulation 132.16 to save Sintra a job.

A, thanks ... I thought that it was most likely to have been drawn from a recent edition of the BB. I fear that I have been a little lazy, not searching it out for myself. That said ... I was always taught at University to quote my sources!
 
A, thanks ... I thought that it was most likely to have been drawn from a recent edition of the BB. I fear that I have been a little lazy, not searching it out for myself. That said ... I was always taught at University to quote my sources!
I thought you were just being polite with a hint of sarcasm.:smile5:
 
I thought you were just being polite with a hint of sarcasm.:smile5:

It did read a little 'haughty' in tone ... I was serious ... I personally have a great deal of respect for those who have 'properly' 'won their spurs' through an apprenticeship if it was worthy of that name! Or indeed those who have faithfully given advice, sharing from their great reservoir's of knowledge and skill, and reasonable derision in equal measure. What Sintra had to say was all that I said it was but until identified as part of a BS it bears the weight of faithful advice, not the weight of a code of practice.
 
It did read a little 'haughty' in tone ... I was serious ... I personally have a great deal of respect for those who have 'properly' 'won their spurs' through an apprenticeship if it was worthy of that name! Or indeed those who have faithfully given advice, sharing from their great reservoir's of knowledge and skill, and reasonable derision in equal measure. What Sintra had to say was all that I said it was but until identified as part of a BS it bears the weight of faithful advice, not the weight of a code of practice.

I am sure Sintra would of expected him to know that too and may of just been trying to kick start His memory.:smile5:
Nice reply by the way.
 
A, thanks ... I thought that it was most likely to have been drawn from a recent edition of the BB. I fear that I have been a little lazy, not searching it out for myself. That said ... I was always taught at University to quote my sources!
I've just had this very argument with a SELECT member GB. He asked me what I'd do and I said walk away if the customer wouldn't have the earthing and bonding sorted. His attitude was you'd never get any work!
 
Obviously if theres no bonding then thats a very different issue, but yes I tend to agree, I must admit, I never used to change consumer units without an isolator fitted first, but now, I just pull the main fuse.
 
Thank you all for your replies. They are all very helpful. I want to do a professional job and feel I have cocked up here. The responses kind of confirm that. Lesson learnt. Thanks for the advice.
 

Reply to Major works notification in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
799
Bit of a rant first to explain the situation:- Effing builders again, I knew there was a reason we hardly ever work for them. We've done a few...
Replies
12
Views
571
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
He's a question for you. What (if any) are the dangers of working INDOORS on an electrical circuit during a Thunderstorm ? Heck you would have to...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock