I realise the OSG is just a guide but it does state in section 4.5 (the green one) that there is no requirement for Main bonding if the incoming service is in plastic.
If there is metal installation within the premises (and plastic incoming) it suggests there should still be Main bonding unless the metal work doesn't test as extraneous.
 
As an aside, if you don't bond the metal pipe work (after plastic), you'll probably or may have to supplementary bond incoming metal pipes into special locations, perhaps ;)
 
As an aside, if you don't bond the metal pipe work (after plastic), you'll probably or may have to supplementary bond incoming metal pipes into special locations, perhaps ;)
if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anyway
 
Protective bonding works with protection a

if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anyway

You type quick, were you poised with a reply :)
 
if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anyway

Forgetting ancillary earthing, boilers etc. How likely are those pipes effectively be bonded to earth? I would suggest, apart from following like sheep, that's the most cost effective way of following reg 528.3.4 that most installs I've seen, seem to follow?
 
Forgetting ancillary earthing, boilers etc. How likely are those pipes effectively be bonded to earth? I would suggest, apart from following like sheep, that's the most cost effective way of following reg 528.3.4 that most installs I've seen, seem to follow?
A measurement can be made to verify the effectiveness of the pipework connected to a main protective bonding conductor

where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition

R =<50 V/Ia in a.c systems
Or
R=<50v/IdeltaN for rcds
 

Reply to New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
921
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock