Might have to up my estimate to 145 posts at this rate.
Your obviously poised to make a definitive statement.
Discuss New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net
Might have to up my estimate to 145 posts at this rate.
Smart Arse.I'd make a wild estimate of 33 posts on this subject by say around 7.16pm
if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anywayAs an aside, if you don't bond the metal pipe work (after plastic), you'll probably or may have to supplementary bond incoming metal pipes into special locations, perhaps
Protective bonding works with protection a
if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anyway
I'm down with the kids when it comes to this mobile texting lark!You type quick, were you poised with a reply
if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anyway
A measurement can be made to verify the effectiveness of the pipework connected to a main protective bonding conductorForgetting ancillary earthing, boilers etc. How likely are those pipes effectively be bonded to earth? I would suggest, apart from following like sheep, that's the most cost effective way of following reg 528.3.4 that most installs I've seen, seem to follow?
Reply to New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net