I like the way 'barriers and enclosures' is ticked but the busbar shield is missing.
Discuss New CU Installation (is it a good job)? in the DIY Electrical Advice area at ElectriciansForums.net
Page 4?
Ze is apparently 0.61 but the Zs readings seem wrong when comparing to R1+R2.Some of the test results look a bit made up, e.g. the Zs values for the radials - but made up by someone who doesn't know what they should look like. I also find Fusebox RCBOs all tend to have somewhat slower trip times than the results, but maybe your electrician had a particularly good batch!
When was it done.As the certificate is a complete counterfeit I don't expect the content to be of any worth. As long as the job itself looks safe I'll move forward.
a week last Thursday - 9 days agoWhen was it done.
Even if the job looks safe, if the circuits were not actually tested, then they could be potentially dangerous. For example, unearthed metal class I light fittings, sockets with polarity errors or no earth, etc. You only find these things out when the testing is done properly.As the certificate is a complete counterfeit I don't expect the content to be of any worth. As long as the job itself looks safe I'll move forward.
Well that Certificate is not in line with the current version of BS7671 and whilst you don't have to follow this standard word for word I would expect the NICEIC to. So are you going to fill us in with the full story as in #1.a week last Thursday - 9 days ago