Hi,

I'm curious to get peoples opinions on this non domestic situation please:

A 20A SP&N radial​
Fed from a 20A MCB​
70 degree singles, grouped in metal trunking fails with 2.5mm singles and even 4mm singles.​

I vaguely remember reading something that, if a cable is loaded to less than 30% its CCC, grouping can be ignored. In this instance the circuit is feeding a door access control panel with a negligible load.

Thanks
 
Fails, as in trips the mcb?
Have you checked IR? Singles in metal trunking may have stripped against a sharp edge, and causing l-e fault.

how packed is the trunking, if grouping may be the issue?
 
Hi,

I'm curious to get peoples opinions on this non domestic situation please:

A 20A SP&N radial​
Fed from a 20A MCB​
70 degree singles, grouped in metal trunking fails with 2.5mm singles and even 4mm singles.​

I vaguely remember reading something that, if a cable is loaded to less than 30% its CCC, grouping can be ignored. In this instance the circuit is feeding a door access control panel with a negligible load.

Thanks
Have a look at this example regarding grouping involving lightly loaded circuits.
image.jpg
 
Fails, as in trips the mcb?
Have you checked IR? Singles in metal trunking may have stripped against a sharp edge, and causing l-e fault.

how packed is the trunking, if grouping may be the issue?

The 2.5mm or 4mm cables fail on CCC on a 20A radial.
[automerge]1587592848[/automerge]
Have a look at this example regarding grouping involving lightly loaded circuits.
View attachment 57653

Thanks Ian1982
 
What is the background to this, are you designing a new circuit?

If the load is negligible why is it being put on a 20A MCB, wouldn't a smaller one be more appropriate.

I can't find it at the moment, but there used to be a line in the regulation stating that conductors operating at less than 30% of their FLC can be excluded from grouping calculations. This is the reason a lot of lighting and small power circuits in commercial installations have 2.5mm lighting conductors and 4mm power conductors, this automatically excludes them from grouping calculations.
 
What is the background to this, are you designing a new circuit?

If the load is negligible why is it being put on a 20A MCB, wouldn't a smaller one be more appropriate.

I can't find it at the moment, but there used to be a line in the regulation stating that conductors operating at less than 30% of their FLC can be excluded from grouping calculations. This is the reason a lot of lighting and small power circuits in commercial installations have 2.5mm lighting conductors and 4mm power conductors, this automatically excludes them from grouping calculations.
If due to known operational loading of Less than 30% of it’s grouped rating then it can be ignored.
I posted an attachment on post no 3
 
What is the background to this, are you designing a new circuit?

If the load is negligible why is it being put on a 20A MCB, wouldn't a smaller one be more appropriate.

I can't find it at the moment, but there used to be a line in the regulation stating that conductors operating at less than 30% of their FLC can be excluded from grouping calculations. This is the reason a lot of lighting and small power circuits in commercial installations have 2.5mm lighting conductors and 4mm power conductors, this automatically excludes them from grouping calculations.

Yeah I'm an M&E building services designer.

I thought about lower the breaker size, but its not something i have seen done before, and it will probably be picked up by the checking consultant.

Thanks
[automerge]1587636519[/automerge]
As Ian mention. I'm just going to omit the group factor.
 
Yeah I'm an M&E building services designer.

I thought about lower the breaker size, but its not something i have seen done before, and it will probably be picked up by the checking consultant.

Thanks
[automerge]1587636519[/automerge]
As Ian mention. I'm just going to omit the group factor.

But surely 20A is not a suitable In if the Ib is as low as you suggest?
What is the Ib for the circuit?
 
If it’s door access, then it will be milli amps at the most unless it’s powering more than one unit , you’ll probably have a 3 amp fused connection unit before the PSU anyway but 20 amps for the ocpd is unnecessary. The psu will have its own ocpd internally as well.
 

Reply to Non Domestic 20A Radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi My consumer unit is located in the garage, the cables are currently clipped to a solid wall above the unit. I am considering putting the...
Replies
18
Views
6K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
1K
C
Hi all, I recently started training to become a domestic installer. I have some practical experience and some knowledge of part P. Also done a...
Replies
8
Views
8K
Chris Norman
C
Hi all, I need some help with working out the correct cable size for some work I'm doing at the moment. I am currently working on testing Mobile...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock