Ze +R1&R2 should be more than Ze mmmmmmmmmm no Ze of .47 yes I know but its not TT its PME,d at the cut out but, Zs at socket .41 SSE have been so hopefully its resolved, anyone else had this
pict
 
Yes, Ze + (R1+R2) does not factor in parallel paths.

Zs is also total impedance rather than Ze + some resistance value. As impedance is an active value, it can vary.

Or at least, that's my take on it :)
 
Ze is < Ze +(R1+R2), however Zs as measured can be < Ze+(R1+R2)
Maximum Zs is Ze +(R1+R2) but measured Zs can be lower.
 
sse had been, and a poor link between neutral and earth at the cut out was the culprit
P
 
  • Like
Reactions: Rpa07
Meter fitters doing loose connections again!
So a variable Earth resistance was the cause of the misaligned readings, Hmm, have to remember that next time I get a high Ze.
 
Mhmm so to unravel that a bit, you @the pict find your Zs lower than Ze. It has been mooted (correctly in my understanding) that paralell paths on actual Zs may account for Zs being lower than Ze. The DNO came and tightened a PME connection at the cut-out. You say this was the reason you had lower Zs than Ze. I am a bit confused as I would have thought you would have a variable reading if the connection of earth to the PME terminal was poor? But is it really the answer, what did your subsequent test reveal, you left the issue open to conjecture with your statement.
 
Last edited by a moderator:
  • Agree
Reactions: westward10
Mhmm so to unravel that a bit, you @the pict find your Zs lower than Ze. It has been mooted (correctly in my understanding) that paralell paths on actual Zs may account for Zs being lower than Ze. The DNO came and tightened a PME connection at the cut-out. You say this was the reason you had lower Zs than Ze. I am a bit confused as I would have thought you would have a variable reading if the connection of earth to the PME terminal was poor? But is it really the answer, what did your subsequent test reveal, you left me hanging a bit with your statement.
Sounds like you're waiting for the Orgasm Vorti
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

the pict

Mentor
~
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
Now surely in the real world
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
11

Thread Tags

Advert

Thread statistics

Created
the pict,
Last reply from
PEG,
Replies
11
Views
1,872

Advert