lofty84

A circuit is protected by a 32A type B breaker. if the value of Ze is 0.8 ohms what will be the maximum allowable value for (R1+R2)


how do I go about finding this in the IEE regs (red one) please ......
 
your max. value for Zs is 1.44ohms ( table 41.3. 32A type MCB). therefore use Zs=Ze+(R1+R2)
 
Last edited:
Its in the regs table 41.3 pg. 56. These values are given at fault conductor operating temp. Where as the ones in OSG are at 80% compared to the regs which are given at normal operating temp.

Sent from my GT-I9100 using Tapatalk
 
cheers telectrix and Si jacc ;-).

So with those details the maximum allowable R1+R2 value is going to be 0.64 ohms

1.44 - 0.8 = 0.64 ohms



well that was nice and easy
 
Last edited by a moderator:
32A x 5 = 160 230/160=1.44 x0.8 =115 ohms is you max allowed take away 0.8 = 0.35 / by cable in table 9A osg will = your length
 
why use the 0.8 value. the question asks for the max. value. the max. value for Zs is 1.44.
 
my answer sheet says the correct answer is 0.64 ohms and that worked with what telectric and SI were saying. i = P/u u have just messed that up lol, how come you are timesing the 32A breaker by 5 snd doing all the other maths.......
 
my answer sheet says the correct answer is 0.64 ohms and that worked with what telectric and SI were saying. i = P/u u have just messed that up lol, how come you are timesing the 32A breaker by 5 snd doing all the other maths.......

.64 ohms if the ze measured is .8 , max r1+r2 depends on what the measured ze is??
 
Cause im good an like to teach you fully ;) and will be teaching electrics when im 55 probably
 
.64 ohms if the ze measured is .8 , max r1+r2 depends on what the measured ze is??

if you don't have the brb to hand, you can calc. the max. ZS for any MCB . it's 230/( 5 x In ) for a B type, for c and d types the factor 5 becomes 10 and 20 respectively.
 
I see so if I had a 40 A type d breaker and I wanted to know the max zs I can go

230/40X20 = 0.2875

doesnt sound right to me ...
 
Last edited by a moderator:
No lofty a type d would be 20 times so it would be 40*20 = 800 and then 230/800 = 0.2875 and table 41.3 is 0.29
 
In the event of an earth fault on the HV side of a substation the LV instillation may be affected by

a)V
b)U
c)I
d)Isqt

im trying to use the contents page in the brb page 3 to find something to go on but cant ...
 
found substations in the index and under reg 442.2 it says either Uf U1 or U2 so it must me U. what does U represent again please ..
 
It is no good us giving you the answers really but a guide have a look and read of section 442 of the BRB
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
one of many to follow Im sure but ......
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
38

Thread Tags

Tags Tags
follow

Advert

Thread statistics

Created
lofty84,
Last reply from
lofty84,
Replies
38
Views
4,371

Advert