sparc

I have a customer wanting to install a couple of very nice, rather classy wall lights above basin in refurbished bathroom in 150 year old property. They're clearly not IPx4 but could easily be converted to 12V, with transformers located in loft space above bathroom.

I'm going through BGB (701.512.2 and 701.512.3) to see if there's any wiggle room here. Apparently not: 701.512.2 says anything in zone 2 needs to be IPx4 - with exception of suitably located shaving points complying with BSEN 61558-2,

If the fitting is SELV the purpose of the IPx4 rating would seem to be only to maintain its reliability, rather than enhance safety - or maybe I'm misunderstanding that part.

Does anyone have experience of putting non-IPx4 rated fittings in zone 2 - in a 'heritage' style hotel, for example? I'm wondering is there are other ways of adapting a fitting that is clearly suited to a period property so that it fully complies with the relevant Regs here.
 
if it's within 0.6m of bath then tell him it's a NO.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
'Period' light fittings in zone 2
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
sparc,
Last reply from
telectrix,
Replies
3
Views
48

Advert