Discuss Periodic inspection (EIC) report questions in the Electricians' Talk area at ElectriciansForums.net
B
Bluebob232
Hi all During r1 r2, ELI and PFC tests of a lighting circuit would it be a problem to leave lamps and ballasts etc in GN3 shows them out but I can't see a problem
It probably shows them with lamps removed as they would have been removed for insulation resistance testing anyway and replaced after completion of the testing.
P.S, r1 and r2 are only done on ring final circuits. Terminolgy is key.:)
Thanks for the replies chaps.I'm am experianced electrician done loads of installs and tests (got my 2391) obviously at the initial verification stage all lamps and accessories are removed and voltage sensitive devices are bypassed not done many periodics. IR tests are done between live conductors and earth as not to blow lamps and ballasts and noted as a limitation and I belive many people do method 2 r2 tests on lighting circuits surely lamps or ballasts won't be affected by r1 r2 test or ELI tests
You shouldn't have problems leaving lamps etc in for continuity & EFLI testing.
On a PIR (EIRC) I personally only do R2 testing to check protective bonding conductors, usually just carry out EFLI on final circuits.
Sent from my iPhone using Tapatalk
Thanks for the reply mate I'm about to undertake a big EICR program on a large site on behalf of a maintenace company not under presure to rush just want to do it correctly and efficiently. Plan is 25 percent accessories check IR between live conductors and earth only. In a lot of places the DBS are that far away a r2 test is impracticle so R1 R2 is best even though r1 r2 and ELI woundnt be affected by lamps being in circuit it just feels wrong what do you guys think of the new eicr's I like how guidence is given on what to look for but having one less code will reduce options a bit. lot of periodics I have seen have that many limitations they are not worth a carrot
Reply to Periodic inspection (EIC) report questions in the Electricians' Talk area at ElectriciansForums.net
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
For example the house today had two lighting T&E in the same MCB. I know it's fine, but as I test both 'radials' where and how do we enter them on...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...