Discuss RCBO not restting in the UK Electrical Forum area at ElectriciansForums.net

You have answered your own question there, the fault is present at 230v and is operating the RCBO, therefore higher than that is not required to trace the fault. I appreciate what 500VDC testing provides, but in the case of locating a fault that is tripping a 30ma RCD, 250VDC is adequate and with no risk.

Think about your response... the rcd is operating with 230v RMS but it stil goes through its waveform and peaks at 320v so if the leakage of a fault only occured at 300v plus then testing at 250v would be insufficient as the rcbo is only seeing the leakage at peak waveform but it will still react.
 
Think about your response... the rcd is operating with 230v RMS but it stil goes through its waveform and peaks at 320v so if the leakage of a fault only occured at 300v plus then testing at 250v would be insufficient as the rcbo is only seeing the leakage at peak waveform but it will still react.

As a theoretical point, what you are saying is electrical fact so I agree with what you are saying. However, what situation can you envisage (in a domestic situation such as the OP's) where there is an insulation fault that would only leak to earth at the peak of the sinewave (320V) enough to operate RCD, yet show a reading on an insulation resistance tester set on 250VDC that would cause no concern to an experienced electrician that there is an insulation issue. On the balance of probabilities, I would say that was a highly unlikely circumstance.
 
As a theoretical point, what you are saying is electrical fact so I agree with what you are saying. However, what situation can you envisage (in a domestic situation such as the OP's) where there is an insulation fault that would only leak to earth at the peak of the sinewave (320V) enough to operate RCD, yet show a reading on an insulation resistance tester set on 250VDC that would cause no concern to an experienced electrician that there is an insulation issue. On the balance of probabilities, I would say that was a highly unlikely circumstance.

You challanged my post, I answered to why we use 500v and not the percentage of it occuring, that fact it can occur justifies my answer and again think about it, any contaminant that might leak on a joint may slowly cause a leakage path and as with most high impedance faults they tend to get progressively worse with time due to carbonisation of the leakage path, believe it or not the circumstances are very common and usually do involve moisture in one form or another.

Have you ever opened a water logged joint tripping an rcd?... you may find it wasn't a one off event that caused the water to build up but progressive until the leakage satified the RCD's operational tripping curve, its the contaminants in the water that create conductance and just splashing water over a L/E joint will not neccessarily trip even a 30mA rcd but leave it and contaminants dissolve into the water and create leakage and tracking and then it satifies the trip value of the RCD.

I design new equipment and machine controls for a living so its my job to understand further than most the circumstances of pollution on electrical joints as thats what you have to deal with in the industrial scene especially my area which is stone cutting, metal shaping and punching and lathes which have steel drums been shaved - all harsh environments for electrical equipment so voltages, IP ratings and knowledge of the contaminants is crucial... this give me an edge on simple domestic problems so Ill stand my ground and say you should be doing standard insulation tests in the OP's case at 500v and its not good advice to suggest 250v.
 
You challanged my post, I answered to why we use 500v and not the percentage of it occuring, that fact it can occur justifies my answer and again think about it, any contaminant that might leak on a joint may slowly cause a leakage path and as with most high impedance faults they tend to get progressively worse with time due to carbonisation of the leakage path, believe it or not the circumstances are very common and usually do involve moisture in one form or another.

Have you ever opened a water logged joint tripping an rcd?... you may find it wasn't a one off event that caused the water to build up but progressive until the leakage satified the RCD's operational tripping curve, its the contaminants in the water that create conductance and just splashing water over a L/E joint will not neccessarily trip even a 30mA rcd but leave it and contaminants dissolve into the water and create leakage and tracking and then it satifies the trip value of the RCD.

I design new equipment and machine controls for a living so its my job to understand further than most the circumstances of pollution on electrical joints as thats what you have to deal with in the industrial scene especially my area which is stone cutting, metal shaping and punching and lathes which have steel drums been shaved - all harsh environments for electrical equipment so voltages, IP ratings and knowledge of the contaminants is crucial... this give me an edge on simple domestic problems so Ill stand my ground and say you should be doing standard insulation tests in the OP's case at 500v and its not good advice to suggest 250v.


You have not answered my post at all and gone all round the houses about the cause of faults and your job experience. You stated (#63) that 250VDC IR was insufficient because the leakage sufficient to operate the RCD my only occur at the peak of the waveform voltage. I am saying that even at 320V with 20-30ma leakage, 250VDC I/R will still show a very low reading which an experienced electrician could determine as an insulation fault with subsequent leakage. I will add that I still use 500VDC where required by BS7671.
 
You have not answered my post at all and gone all round the houses about the cause of faults and your job experience. You stated (#63) that 250VDC IR was insufficient because the leakage sufficient to operate the RCD my only occur at the peak of the waveform voltage. I am saying that even at 320V with 20-30ma leakage, 250VDC I/R will still show a very low reading which an experienced electrician could determine as an insulation fault with subsequent leakage. I will add that I still use 500VDC where required by BS7671.

Yes most of the time even at 250v IR faults would show but your not appreciating dialectric properties of materials here, insulation breakdown is not linear therefore you cannot say that 250v IR test would expose a issues proportionally as that of a reading using 500v. It may be the case that the issue can only be detected at say 300v and remain undetected below that, this could lead to a false positive if testing on 250v, the value may show lower than expected but well within concerning values but at 500v you may see a significant breakdown in IR.

Even though many IR issues can clearly be identified at both test voltages due to the severity it remains the case that you can have a breakdown occuring at only close to peak voltages, now in the days before rcd's were thrown at every situation this would just be a matter of time before the breakdown got worse to cause noticable problems and a sparky called in, rcd's now have such sensitivity that adding general background leakage of devices its possible for the rcd to be sensitive to say 5-10mA of a fault where the rest is made up of electronics goods and other designed leakages, this in itself can make for a device able to pick up peak only issues that cannot be detected at a lower test voltage, also to note is the conductor temp' - because you are not really putting any current down the cable the conductors will not be subject to the same conditions as when loaded so the 500v also compensates for this too.
 

Reply to RCBO not restting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, just a quick one to ask about an issue I'm having with my EV charger. I'll give a little background first but ultimately I want to know if...
Replies
11
Views
2K
Last week I took the opportunity of having the mains power off to test the RCBOs in a Wylex Consumer Unit, fitted nearly 5 years ago, which has...
Replies
2
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
👋 First time poster here. My name is Melissa and I’m asking for advice regarding my mom and stepdad’s home. He tried for 4 days to work the...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock