some dmm's can do ir as wellGood luck when you get an insulation fault!
Discuss RCBO not restting in the UK Electrical Forum area at ElectriciansForums.net
some dmm's can do ir as wellGood luck when you get an insulation fault!
You have answered your own question there, the fault is present at 230v and is operating the RCBO, therefore higher than that is not required to trace the fault. I appreciate what 500VDC testing provides, but in the case of locating a fault that is tripping a 30ma RCD, 250VDC is adequate and with no risk.
Think about your response... the rcd is operating with 230v RMS but it stil goes through its waveform and peaks at 320v so if the leakage of a fault only occured at 300v plus then testing at 250v would be insufficient as the rcbo is only seeing the leakage at peak waveform but it will still react.
So do MFT's, they do it all. You said "id use my fluke dmm on continuity. it goes a lot lower than the continuity on a megger"
As a theoretical point, what you are saying is electrical fact so I agree with what you are saying. However, what situation can you envisage (in a domestic situation such as the OP's) where there is an insulation fault that would only leak to earth at the peak of the sinewave (320V) enough to operate RCD, yet show a reading on an insulation resistance tester set on 250VDC that would cause no concern to an experienced electrician that there is an insulation issue. On the balance of probabilities, I would say that was a highly unlikely circumstance.
You challanged my post, I answered to why we use 500v and not the percentage of it occuring, that fact it can occur justifies my answer and again think about it, any contaminant that might leak on a joint may slowly cause a leakage path and as with most high impedance faults they tend to get progressively worse with time due to carbonisation of the leakage path, believe it or not the circumstances are very common and usually do involve moisture in one form or another.
Have you ever opened a water logged joint tripping an rcd?... you may find it wasn't a one off event that caused the water to build up but progressive until the leakage satified the RCD's operational tripping curve, its the contaminants in the water that create conductance and just splashing water over a L/E joint will not neccessarily trip even a 30mA rcd but leave it and contaminants dissolve into the water and create leakage and tracking and then it satifies the trip value of the RCD.
I design new equipment and machine controls for a living so its my job to understand further than most the circumstances of pollution on electrical joints as thats what you have to deal with in the industrial scene especially my area which is stone cutting, metal shaping and punching and lathes which have steel drums been shaved - all harsh environments for electrical equipment so voltages, IP ratings and knowledge of the contaminants is crucial... this give me an edge on simple domestic problems so Ill stand my ground and say you should be doing standard insulation tests in the OP's case at 500v and its not good advice to suggest 250v.
You have not answered my post at all and gone all round the houses about the cause of faults and your job experience. You stated (#63) that 250VDC IR was insufficient because the leakage sufficient to operate the RCD my only occur at the peak of the waveform voltage. I am saying that even at 320V with 20-30ma leakage, 250VDC I/R will still show a very low reading which an experienced electrician could determine as an insulation fault with subsequent leakage. I will add that I still use 500VDC where required by BS7671.
Love this site the op has long gone now the usual suspects battle it out to see who has the biggest wang.