Hi all.

I'm getting abit confused. Help would be appreciated.

Was called to a customer who had lights dimming and kettle not working.

Arrived and found TT sytem with in line Voltage operated Earth Leakage device between cutout and fuse box.
The device was found to be faulty, large voltage drop reduced the supply voltage down to 120V so replaced this with a DB 100A isolation switch as a temporary measure, then to return with an 30mA RCD to offer earth faualt protection. Recommende a new 17th edit CU to comply but they weren't keen on the idea. So told em if RCD trips all circuits will become unoperational.

Tested RCD....just wouldnt trip. suspected a neutral to earth fault.

Removed all neutrals and found the lighting circuit to be culprit.

With a time limit of 1 hour to hunt down the cause......I figured not much hope.


Anyway Found that on removing the lighting circuit neutral the RCD tripped as the neutral was removed from the neutral bar.

On attempting to reset RCD it would not reset. But did reset once the neutral was replaced

Anyone know why please.

Thanks in anticipation
 
If it wouldn't trip I would think it is unliely to be an N/E fault or it wouldn't set in the first place.

If it won't set when the light neutral is out (I hate to say this because it sounds so b*****y stupid), is the light neutral acting as the supply neutral? Many rcd's wont set if they haven't got a neutral.
 
As above^^^^^^^^^^^^^^^^.

I wonder whether the 120V was you thinking you were testing between live & neutral when in fact you have no neutral and picking up live to earth through the neutral of one of the circuits. With everything disconnected check L - N and see if you have any voltage.
 
I'm wid you Top Cat I also think that there is in fact no neutral on the supply. It only gets a neutral if the lighting cct neutral is connected because the lighting cct has an earth fault on it. Try dising the Lighting cct and then measure the voltage at the supply, you may find that you have zero or close to it.
 
I do remember that when I started my apprenticeship there were lots of very old installations that were double pole fused, yes double pole fused. It was common for people to mix up neutrals and cross them and cause all sorts of problems not unlike the one you have.
Best of luck Philpot
 
Hi ACVC One that I remember was when the lighting CCts, Upstairs and downstairs, had the neutrals crossed/joined. This usually happened around the hall and staircase lighting. That was because the 2 way switches were in common conduit. If you pull, what you think is the L + N fuse for a cct then some lights go out but you could find a lethal voltage on the cct if certain lights were on. It was also possible to get lights in series so they were half brilliance. ....It's easier to draw than describe. The main thing was that they realised that neutral fuses were a bad idea and it was never contemplated again on any cct that has an earthed neutral.
There are however CCts that do not have an earthed neutral, like ships. This is a different story when you have to check every day or monitor for earth faults ( well that was when I was at sea). It is possible to have an earth fault on both the live and neutral at the same time.

Regards Phil
 

Reply to RCD wont trip... tehn trips.....then wont reset... Whats going on please? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
404
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock