Had the plumber in today and have come across a problem with my stopcock. It basically won't close, stays open so he was going to replace it. As it's in a very awkward place he suggested repositioning it to a better place that's more accessible, ie underneath the sink. Now there's a 10mm earth on the consumer side which is fine but if this stopcock is to be done away with & repositioned, will the 10mm earth need to also be repositioned so it's on the consumer side of the new stopcock or is it fine to leave it where it is?
 
Yes of course
 
if the stopcock is otherwise OK, apart from not closing, why not leave it in and fit a second one after it? sounds a much simpler job and the bonding can stay as is.
 
  • Like
Reactions: 2 people
Do they intend to use plastic pipework or plastic stopcock or will it all be copper and brass? If plastic you may need to reassess what items in the bathrooms require bonding.

Where's Cockburn when you need him? ;)
 
  • Like
Reactions: 4 people
Had the plumber in today and have come across a problem with my stopcock. It basically won't close, stays open so he was going to replace it. As it's in a very awkward place he suggested repositioning it to a better place that's more accessible, ie underneath the sink. Now there's a 10mm earth on the consumer side which is fine but if this stopcock is to be done away with & repositioned, will the 10mm earth need to also be repositioned so it's on the consumer side of the new stopcock or is it fine to leave it where it is?

So this seized open stopcock is going to be abandoned and a new one fitted a bit further downstream??

There's nothing wrong with that and I've done it myself. Why not just leave your bond where it is and if anybody wants to argue the ---- tell them that one is the main stopcock and the one under the sink is a secondary one.
 
  • Like
Reactions: 3 people
So this seized open stopcock is going to be abandoned and a new one fitted a bit further downstream??

There's nothing wrong with that and I've done it myself. Why not just leave your bond where it is and if anybody wants to argue the ---- tell them that one is the main stopcock and the one under the sink is a secondary one.

Original is that G
 
  • Like
Reactions: 1 person
Or....if it serves the purpose...keep yer mitts off it.:)
 
  • Like
Reactions: 1 person
if the stopcock is otherwise OK, apart from not closing, why not leave it in and fit a second one after it? sounds a much simpler job and the bonding can stay as is.

Yes that's what the plumber has done. It's all copper from the old stopcock to the new one so bonding will be ok to leave.

Do they intend to use plastic pipework or plastic stopcock or will it all be copper and brass? If plastic you may need to reassess what items in the bathrooms require bonding.

Where's Cockburn when you need him? ;)

Copper. Just going to leave current one in.

Could you move the bonding cable to where the new isolator is going to be?

Would have to be rewired.

So this seized open stopcock is going to be abandoned and a new one fitted a bit further downstream??

There's nothing wrong with that and I've done it myself. Why not just leave your bond where it is and if anybody wants to argue the ---- tell them that one is the main stopcock and the one under the sink is a secondary one.

Looks like this shall be the plan.

Thanks for your help folks.
 
  • Like
Reactions: 1 person
and don't forget to bond the sink. :45:
 
The regulations state that MEB connection to water service shall be made as near as practicable to the point of entry.

There is NO mention of stopcocks.

It is very simple.
 
quack, quack!
 
never heard of it.though dysentry was a US soap with that slapper collins.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Reposition water service earth bond.
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
SSE,
Last reply from
Geordie Spark,
Replies
20
Views
2,629

Advert