Hi all hoping you use can help, came across an issue when carrying EIC on new build installation that was wired by another spark and I am testing it. The strangest thing is there is 3 rings in the house that have been wired, kitchen, upstairs and downstairs. But there is also another ring wired back to consumer unit. So all rings have got end to end continuity and figure of eights completed with all sockets given same result with 0.03 of difference at some points. But there is another ring that is wired that doesn’t seem to be connected to anything as I have went to all points in the house and this ring is not connected. I think On 1st fix stage this ring has been pulled in has a loop on it but is not going/connecting to anything. Has powered up board all circuits on and this ring does not have power on it, so I have not connected to consumer unit and have put ring into connector strip at back of board. Just thinking would it be best if this ring was connected to the earth bar or would leaving in connector strip be better ? Thanks in advance ?