Hi Guys

A customer wants to replace a class 2 fitting with a class 1 the lighting circuit does not have a CPC, I want to run a seperate 1.5mm CPC but as its less than 4mm does it need mechanical protection? And is it acceptable to only run it to the fitting in question?

Your help with this would be appreciated

Many Thanks
T&E
 
Not as good on the reg's as some of the guys on here but i would say yes you do need mechanical protection for 1.5mm so why not just run a 4.0mm?

As for 2nd part of question i would say yes.

If i am wrong we will know very soon!
 
  • Like
Reactions: 2 people
to comply, 543.1.1, so 4mm
 
  • Like
Reactions: 2 people
There isn't anything in the regs that says earth wires neeed mechanical protection when its not buried.
 
  • Like
Reactions: 1 person
Hi Guys

A customer wants to replace a class 2 fitting with a class 1 the lighting circuit does not have a CPC, I want to run a seperate 1.5mm CPC but as its less than 4mm does it need mechanical protection? And is it acceptable to only run it to the fitting in question?

Your help with this would be appreciated

Many Thanks
T&E

you can clip the single earth or trunking upto the ceiling soon as you are under the upstairs floor your ok
 
yes. you could argue that under the floor, it's mechanically protected by the enclosure of the building fabric.
 
Not as good on the reg's as some of the guys on here but i would say yes you do need mechanical protection for 1.5mm so why not just run a 4.0mm?

As for 2nd part of question i would say yes.

If i am wrong we will know very soon!

HEY TC
have you got your stuff ready for your big day tomorrow
 
in a real life situation, i'd be inclined to run 1.5mm. remember that BS7671 is not statutory and if you consider that 1.5mm will provide adequate fault protection, then go ahead. tin hat on.
 
  • Like
Reactions: 1 person
Use 4mm, you only need to provide a cpc to that fitting as long as the rest are still class 2...
well i`d be asking what the intentions are in future as regards the other fittings.....its just that they may like that class 1 so much that they decide to start replacing these class 2s with class 1s......without upgrading the wiring to suit....
 
  • Like
Reactions: 1 person
well, if the customer does that after having been told not to fit classI fittings without providing a cpc, then the darwin theory springs to my mind.
 
  • Like
Reactions: 1 person
well, if the customer does that after having been told not to fit classI fittings without providing a cpc, then the darwin theory springs to my mind.
unskilled/uninstructed person/s not under supervision Tel.....in other words..they cant be trusted....could make a note of it...
 
  • Like
Reactions: 1 person
hi guys

Just one thing as stated i will run 4mm, but this cable will take a completely different route to the line & neutral at the board and at the JB by light fitting it will be obvious that its CPC but through out the rest of the run it go any where whats to stop someone else coming along and thinking its an old undersized bonding conductor and cutting it out!!
Many Thanks
T&E
 
Depends on route. If coming thro loft, down inside of airing cupboard tucked by architrave, then under floor to light fitting, then I'd use a bit of 1.5.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Running Seperate CPC to light fitting HELP PLEASE
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
T&Earth,
Last reply from
SPARTYKUS,
Replies
17
Views
3,013

Advert