Discuss So I'm In A House Today And I Notice A 30ma Rcd On The Wall in the UK Electrical Forum area at ElectriciansForums.net

OnlQQker

Esteemed
Reaction score
1,273
It feeds an outdoor socket. On the comsumer unit is a 60ma Rcd and everything is covered by this.

I'm just wondering if the 30ma Rcd would trip before the 60ma Rcd trips (if that makes sense)

It's just my mind wondering about stuff, the chap who owns the house said it's never tripped out, yet I wondered if 30 ma would trip first because it's lower than the 60ma in the consumer unit. To me I'm guessing it would?
Anybody helping explain this would mean I might get some sleep tonight without thinking about it in bed, I've tried searching the net for the answer but no luck! :D
 
Depends totally on the makes of the rcds

Once the current gets around 5-10x the trip setting, they don't get any quicker.

So if the 30mA one trips in 10.4mS (5x), but the 60mA goes in 10.2mS (5x), then the 60 would trip first due to the fault current normally being well above both mcb's 5x values; as the fault current is usually many amps (to meet normal disconnection times) so both are in a race to trip, and once they have started they will finish...

So whichever one trips first is purely academic as they will both operate in similar times
 
60mA RCD? are you sure?
Not now, it was only a glance because high up. Will make an excuse to have a look again tomorrow. Now if it is a 30ma they will both trip right, or would the closest one go first?

Old Hager consumer unit (approx. 10 years old) , kitchen ring, upstairs ring, down ring, garage, cooker. Lighting is on an RCBO
[automerge]1583438315[/automerge]
Depends totally on the makes of the rcds

Once the current gets around 5-10x the trip setting, they don't get any quicker.

So if the 30mA one trips in 10.4mS (5x), but the 60mA goes in 10.2mS (5x), then the 60 would trip first due to the fault current normally being well above both mcb's 5x values; as the fault current is usually many amps (to meet normal disconnection times) so both are in a race to trip, and once they have started they will finish...

So whichever one trips first is purely academic as they will both operate in similar times
Many thanks for explaining that Julie. It was one of them curiosity things more than anything! :)
 
Phoenix used to supply 60mA rcds, but just din rail, and not the normal thing to put in a hager cu.

There is absolutely no coordination or discrimination between rcd unless there is a time delay, both will trip in around the same time,
 
Ramp test any 30mA rcd and you’ll get different measurements. There’s no reasoning if one is closer to the load or not as to which would trip first.
And if one is “aged” or otherwise of a lesser quality, the tripping threshold could change day by day. As long as it trips before 30mA is reached
 
I have two RCD in line one at the main DB and two RCBO Lights and socket, in the garage. The garage is 20m from the house on TN-C it trips in the garage if tested. How about that! And lets not get into whys or wherefores on the matter it is just a fact and that is how it is.
 
I have two RCD in line one at the main DB and two RCBO Lights and socket, in the garage. The garage is 20m from the house on TN-C it trips in the garage if tested. How about that! And lets not get into whys or wherefores on the matter it is just a fact and that is how it is.
aha. trips when tested. may not do that in a real fault scenario.
 
I have two RCD in line one at the main DB and two RCBO Lights and socket, in the garage. The garage is 20m from the house on TN-C it trips in the garage if tested. How about that! And lets not get into whys or wherefores on the matter it is just a fact and that is how it is.
Thanks for this reply.
[automerge]1583444517[/automerge]
aha. trips when tested. may not do that in a real fault scenario.
I thought testing was to stimulate real fault scenarios?
 
it is to simulate, but simulation does not always work in real life. viz. Titanic.
 
Not now, it was only a glance because high up. Will make an excuse to have a look again tomorrow. Now if it is a 30ma they will both trip right, or would the closest one go first?

An RCD mainswitch will probably go first as it will likely have some normal earth leakage from all of the connected circuits biasing it to trip first.
 
An RCD mainswitch will probably go first as it will likely have some normal earth leakage from all of the connected circuits biasing it to trip first.

Not always. As I mentioned before, an rcd could trip at anything up to 30mA.
Circuit could trip at 19, main switch at 29... fault current may sit at 24..

It’s possibly down to whichever rcd is the most awkward to reset.
e.g a static caravan has an rcd mainswitch in its consumer unit, there is also a 16A rcbo in the hookup box outside.
if there’s a fault, it’s 9/10 that it’s outside that trips..... in the middle of the night...... when it’s raining.....
 

Reply to So I'm In A House Today And I Notice A 30ma Rcd On The Wall in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

When I notice one of those new lodge sites. A bit like the old caravan parks but way more modern. Composite cladding, plastic ridged rood tiles...
Replies
5
Views
982
Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
5K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
No lighting has been changed in the house for at least 12 months. Last night a small pop similar to that of a small firework in the distance came...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock