Discuss solar p.v earthing in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
P
Phantasmagoric
can any one advise does the armouring on swa cable on dc side does it need earthing also does cable tray on dc side need earthing and what about containment on a roof is that left floating getting told different answers of different people people.and 1 more thing is there some kind of single flex to connect between inverters and isolators that goes up to 10mm. any one
Is the inverter transformer-less or not?
If the inverter has a transformer then you don't need to earth anything on the DC side.
If the inverter does not have a transfomer then...
Rule of thumb CPC half of line conductor but as it's outside minimum 4mm
Bond the mounting (all significant rails) together.
Bond the armour of the SWA together with the frame to a new TT earth electrode
Do not bond the SWA armour to the earth terminal on the inverter as this is (normally) within the equipetential zone of the property.
All the outside gear bonded together and taken to the new earth electrode.
Test new earth to AC line as normal to determine Ze of new electrode normal rules apply <100ohms (200ohms permitted)
That's how I understand it, anyone got any different ideas?
Reply to solar p.v earthing in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Hi installing my first solar PV on my own home before starting the courses next year and need some advice on earthing PV. System 6kw solar PV - 2...
7K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...