i'd do as you say for DB2, but if and when you come to fit DB3, feed the tails from the henly blocks at the intake with a 2nd 63A switch fuse. then you won't have 2 63A fuses in series. and as biff says, max. 40A MCBs in DB2 and DB3.
 
i'd do as you say for DB2, but if and when you come to fit DB3, feed the tails from the henly blocks at the intake with a 2nd 63A switch fuse. then you won't have 2 63A fuses in series. and as biff says, max. 40A MCBs in DB2 and DB3.

that is the logical way forward,thank you for your help guys.
 
As you’ve applied diversity to the two sub boards loading and added to a real reading of 50A for the main board. You’re in trouble (in theory).

The thing I love about diversity is it’s the biggest load of codswallop out! BS88’s are about as subtle as a brick, that’s why I like them as well.
 
As you’ve applied
diversity to the two sub boards loading and added to a real reading of
50A for the main board. You’re in trouble (in theory).

The thing I love about diversity is it’s the biggest load of codswallop
out! BS88’s are about as subtle as a brick, that’s why I like them as
well.

diversity has been applied correctly and not in the manner you have incorrectly presumed
 
diversity has been applied correctly and not in the manner you have incorrectly presumed

What method of diversity have you applied to these separate CU installations??
I think Tony meant, that applying diversity is often a hit or miss affair, and unless you have many years under your belt in the industry, it'll be more often a miss than a hit!! The maximum demand diversity formulas you'll find quoted in BS7671 are the next best thing to being totally useless!!
 
Have to agree here; I split my house into loads of seperate RFC & lighting circuits. Went from a 5 way 3036 to a 12 way CU and all of a sudden I need my own power station!!!! But no additional demand. Crazy!
 
What method of diversity have you applied to these separate CU installations??
I think Tony meant, that applying diversity is often a hit or miss affair, and unless you have many years under your belt in the industry, it'll be more often a miss than a hit!! The maximum demand diversity formulas you'll find quoted in BS7671 are the next best thing to being totally useless!!

i have already said that diversity has been applied to the design of the installation,the way it has been calculated for this installation is as follows...
i have counted the lighting points and made a calculation based upon the presumed load,as opposed to just calculating 66% of the 6 amp circuit...i presume this is what you were referring to when you asked which method was used to calculate diversity?...same method of calculation was used for cooker and ring circuits...etc...(with their respective diversity allowances).
Is this acceptable?
 
i have already said that diversity has been applied to the design of the installation,the way it has been calculated for this installation is as follows...
i have counted the lighting points and made a calculation based upon the presumed load,as opposed to just calculating 66% of the 6 amp circuit...i presume this is what you were referring to when you asked which method was used to calculate diversity?...same method of calculation was used for cooker and ring circuits...etc...(with their respective diversity allowances).
Is this acceptable?

In a word ...NOPE!!

Calculating accurate max demand and diversity is an art, which takes a good amount of experience to master. Their are rule of thumb methods that many use, (often, myself included) but even those are not what you would or could call accurate!!
 
I'll avoid the diversity argument because I think Tony and E54 have a handle on that thorny issue already, and I personally hate the darned thing as i feel, like them two, it is exceptionally rarely applied accurately or properly and the blame for that lays squarely with the IET.

I am curious as why you have not suggested to your client to up-rate the supply to 125A (The majority of domestic installs are capable of this) and is a cheap upgrade. Then the out from this should go (If only one meter installed) to the meter, then to a DB with 1 Double Pole 80A MCB Type B installed for the main flat and two Double Pole 63A MCB's Type B installed, one for each living unit and you then run a sub-main/tails from this board to the individual consumer units. If at some point the individual units get their own meter then it is a simple matter to install sub meters to the outgoing ways just as we do in commercial sublet units but you keep the main meter to ensure all meter readings actually add up...

You end up with a nice neat and clean installation, fully compliant and you also stop one person overloading things to the point of killing all...(in theory anyway)
 
That sounds like the neatest way of doing it to me! Also probably the most functional way too in regards to adding additional meters at a later date.

I have never heard of a domestic i stall being upgraded to 125A though. Is it just a phonecall to the DNO and if so what is the cost? That is some valuable information right there Outspoken.
 

Reply to Sub board from sub main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
502
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
499
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
324
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Can you feed a consumer unit from another consumer unit, It would be supplied by a non RDC protected MCB. Is this allowed as I have always seen...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock