That sounds like the neatest way of doing it to me! Also probably the most functional way too in regards to adding additional meters at a later date.
I have never heard of a domestic i stall being upgraded to 125A though. Is it just a phonecall to the DNO and if so what is the cost? That is some valuable information right there Outspoken.
Very common in London and some bigger towns, a lot of modern town houses (The 3 Floor type) have 125A heads, although I am sure the availability will vary by the DNO, cost and most importantly, the supply cable being capable of being uprated.
I have done this on small commercial installs, but the heads are the same, and for the most part so are the cable sizes, and usually it takes a phone call, a form and a fee. Last time I did this it costs about £200, but I do know that in London domestics would be done for free, but this was more than a decade ago so it is likely to have changed significantly, perhaps one of the sparks who has done this recently will pop by and give you some up to date information on this, but I would suggest a call to the DNO would be the first point of contact and they can tell you if it is possible on your supply, if they say NO then everything we say here is moot.
I'll avoid the diversity argument because I think Tony and E54 have a handle on that thorny issue already, and I personally hate the darned thing as i feel, like them two, it is exceptionally rarely applied accurately or properly and the blame for that lays squarely with the IET.
I am curious as why you have not suggested to your client to up-rate the supply to 125A (The majority of domestic installs are capable of this) and is a cheap upgrade. Then the out from this should go (If only one meter installed) to the meter, then to a DB with 1 Double Pole 80A MCB Type B installed for the main flat and two Double Pole 63A MCB's Type B installed, one for each living unit and you then run a sub-main/tails from this board to the individual consumer units. If at some point the individual units get their own meter then it is a simple matter to install sub meters to the outgoing ways just as we do in commercial sublet units but you keep the main meter to ensure all meter readings actually add up...
You end up with a nice neat and clean installation, fully compliant and you also stop one person overloading things to the point of killing all...(in theory anyway)
thank you outspoken for your input,all things considered uprating main fuse to 125A would be the ideal solution (dno price and supply cable capability permitting)..further investigation required on this one and again i thank all contributors to the thread, i am not 100% sure as to best way to proceed so the best thing to do is check check and check again...that is a big part of being electrically competent,in that you recognise your limitations and address them...hence the question being asked!!
- - - Updated - - -
In a word ...NOPE!!
Calculating accurate max demand and diversity is an art, which takes a good amount of experience to master. Their are rule of thumb methods that many use, (often, myself included) but even those are not what you would or could call accurate!!
your views are entirely valid,however there is guidance in the appropriate regulations and literature in regard to the application of diversity and the fact that there is widespread misunderstanding in the industry and learning institutions does not negate its usage nor validity. Personally i dont find the concept or the application of diversity to be all that challenging,agreed there is a need for experience but you will not get experience without practising!! i do not mean to suggest i know it all about diversity but i am saying i dont understand the dislike of it by many sparks? its application and intended use is apparent to me.
Surely you would need a main isolator? I dont recall reading about one in these posts. Forgive me if I've missed this and you have allowed for it.
A little conundrum for you all on diversity.
Two 1600A incomers (open bus)
Outgoing:
1 X 1200A
9 X 600A
6 X 400A
3 X 200A
We never blew a fuse in the 23 years I was there after I installed it!
Outgoing:
1 X 1200A
9 X 600A
6 X 400A
3 X 200A
That is pretty common..
We just installed the following...
Dual 4000A Feeders to the Bus bars in the switchgear..
Outputs..from each (as they are duplicates) so below is just the A stream (The B listed are because there are two on each stream of some.)
Feed to UPS A = 1600A
Feed to UPS B = 1600A
Feed to Mech A Panel = 1200A
Feed to Mech B Panel = 1200A
Feed to DX Panel = 1200A
Feed to GLP Panel = 900A
Feed to Underground Services = 800A
Feed to External Services = 600A
Feed to Gen A = 200A
Feed to Gen B = 200A
Feed to Gen C = 200A
Feed to Ancillary Services = 200A
Well i can tell you for an absolute certainty, that not a single electrical Design or Consultant Engineer would ever think about using the data fond within BS7671 or any of it's GN's on the subject!! The figures you will end up with, will always be so far out of this world and pretty much useless to man or beast!!
Try using those max demand/diversity on your own house, and you'll very quickly see exactly what i mean!! The chances are, you will end up with a figure, that is well above the DNO's cut-out fuse rating!!
Sub board from sub main
nottz_spark,
Engineer54,