Thanks for reply Everyone


Garage /outbuilding end

Swa is coming out of concrete but too short too gland directly into the Metal CU so
the Swa has been glanded into a metal adaptable box then then outer sheathing removed to show the three single cores . two of them have been run ( for about 10 inches )into seperate henley boxes . third core used as earth to garage cu . swa and henleys all trunked over .

then 25mm tails to the consumer unit length about 450mm each.

the consumer unit in garage is a crabtree starbreaker and has two 6amp rcbos / and two 32 amp rcbos protecting the outgoing circuits .


main House end

The utilty supply comes from the Main Fuse which is sealed but i suspect a 80amp .
This goes off to a 100amp isolator which the utility company fitted .
From here we have 25mm tails to henley blocks , from the henley blocks we then have 25mm tails to the main house consumer unit . ( 7 circuits protected by Rcbos)

The earthing Is TN . 16mm earth wire from utilty supplier to earth block . then 16mm to house CU 10mm to gas 10mm to water .

the SWA run starts here
I wanted to run two 25mm tails from henley to a Wylex 100amp isolator ( couldnt find a lower amp one) connect the Swa which runs to the garage
OK

There are a number of issues, if you have used an isolator, this is merely a switch, and provides no protection to the cable.

This cable must be provided with both overload and fault protection, usually via a fuse switch (assuming swa all the way).

One way of back-checking your work, is to imagine what an experienced person would assess the work both as an initial installation and as an eicr. If you did this it would attract a C2 for both missing fault and for missing overload protection (2×C2).

I still don't quite understand the boxed in part, if this is proper trunking then that's one thing, however if not and it's a matter of being behind metal/plastic/timber covering that looks architectural then there are further issues, firstly as the cable has only a single layer of insulation this would attract a C2 - a second layer must be applied, a colouring sheath would not meet the requirements as it should not be removable without tools/destruction and is generally not of the required thickness/insulation.

In addition, now this cable is hidden less than 50mm in the building structure, rcd protection is required, some would code this as a C2 some C3, I would normally consider it C3, however as a substantial supply to a sub-main I would give this a C2 - driving a nail into a 1mm^2 - 2.5mm^2 cable protected by a 6A/32A mcb is one thing, into a 16mm^2 unprotected cable is another!

If it's a matter of a few ft, can you not move the garage cu? Or install proper steel conduit/trunking
 
As @Julie. points out, can you enclose any extension in proper earthed metal conduit or trunking?

If extending SWA as @littlespark suggest then you can use these sort of joints that are suitable even for directly buried cables for 16mm 2-core:
Or for 16mm 3-core:
But if doing so then please carefully read and follow the joint instructions fully!
 
As @Julie. points out, can you enclose any extension in proper earthed metal conduit or trunking?

If extending SWA as @littlespark suggest then you can use these sort of joints that are suitable even for directly buried cables for 16mm 2-core:
Or for 16mm 3-core:
But if doing so then please carefully read and follow the joint instructions fully!
I think he said he's using 3 core and I'd also agree this is a good way forwards.
Worst one I ever had to do was in a deep muddy puddle when a plumber got excited with a mini digger. Most annoying was it was a cable I'd installed myself 12 months earlier, and even though covered in cable bricks and marker tape he still tore it up so badly a new section was needed....
1619768576928.png
1619768654038.png
 
Thanks for reply Everyone


Garage /outbuilding end

Swa is coming out of concrete but too short too gland directly into the Metal CU so
the Swa has been glanded into a metal adaptable box then then outer sheathing removed to show the three single cores . two of them have been run ( for about 10 inches )into seperate henley boxes . third core used as earth to garage cu . swa and henleys all trunked over .

then 25mm tails to the consumer unit length about 450mm each.

the consumer unit in garage is a crabtree starbreaker and has two 6amp rcbos / and two 32 amp rcbos protecting the outgoing circuits .


main House end

The utilty supply comes from the Main Fuse which is sealed but i suspect a 80amp .
This goes off to a 100amp isolator which the utility company fitted .
From here we have 25mm tails to henley blocks , from the henley blocks we then have 25mm tails to the main house consumer unit . ( 7 circuits protected by Rcbos)

The earthing Is TN . 16mm earth wire from utilty supplier to earth block . then 16mm to house CU 10mm to gas 10mm to water .

the SWA run starts here
I wanted to run two 25mm tails from henley to a Wylex 100amp isolator ( couldnt find a lower amp one) connect the Swa which runs to the garage
Have you got a pic? Hard to visualise
 
OK

There are a number of issues, if you have used an isolator, this is merely a switch, and provides no protection to the cable.

This cable must be provided with both overload and fault protection, usually via a fuse switch (assuming swa all the way).

One way of back-checking your work, is to imagine what an experienced person would assess the work both as an initial installation and as an eicr. If you did this it would attract a C2 for both missing fault and for missing overload protection (2×C2).

I still don't quite understand the boxed in part, if this is proper trunking then that's one thing, however if not and it's a matter of being behind metal/plastic/timber covering that looks architectural then there are further issues, firstly as the cable has only a single layer of insulation this would attract a C2 - a second layer must be applied, a colouring sheath would not meet the requirements as it should not be removable without tools/destruction and is generally not of the required thickness/insulation.

In addition, now this cable is hidden less than 50mm in the building structure, rcd protection is required, some would code this as a C2 some C3, I would normally consider it C3, however as a substantial supply to a sub-main I would give this a C2 - driving a nail into a 1mm^2 - 2.5mm^2 cable protected by a 6A/32A mcb is one thing, into a 16mm^2 unprotected cable is another!

If it's a matter of a few ft, can you not move the garage cu? Or install proper steel conduit/trunking
Thanks again everyone have been very helpful and have brought up some issues which i will adapt .

---house end do not use 100amp isolator ,instead replace with a 63 amp wylex fused switch will protect the live feed of the SWA .

--- garage end the wiring is already in situ so i dont fancy digging up or extending CU . so i will use a large adapatable box to put the exposed single cores and henley boxes in . That should be up to regulations ?


--i was understanding that i dont need RCD protection for the SWA as the armor is earthed at both ends. Will that not be sufficient ?
 
Ahh okay so if put in large adapatable box of metal construction next to the consumer unit will that be appropriate.?
Sounds ok to me.
If I was having to sort that out I'd probably go for slightly larger box than that one, longer double insulated tails (supported), appropriate grommet, and solder/crimp, tape and heat shrink the joints inside the box, and dispense with the Henleys.
But just throwing a metal box or trunking around it would achieve the same.
 
Maybe not quite how I ould have done it myself, but the only thing I can see that is non compliant is the lack of a double sheath on the exposed SWA conductors.
If you have any left over 16mm2 or 25mm2 tails, suitable lengths of the outer sheath slid off and slipped over the exposed brown and grey ends of the SWA will do the job.
 
You can't possibly leave it like that aside from looking awful those conductors are not enclosed. No amount of sleeving will make any difference as you will never be able to completely cover them it will always be exposed where they exit the cable. Crimp some 16.0 6181Y within the adaptable box then bring out through a gland.
 
Sounds ok to me.
If I was having to sort that out I'd probably go for slightly larger box than that one, longer double insulated tails (supported), appropriate grommet, and solder/crimp, tape and heat shrink the joints inside the box, and dispense with the Henleys.
But just throwing a metal box or trunking around it would achieve the same.
Great thanks
 
Why will the ends be exposed anymore than the ends of tails when they connect to service blocks at the DNO service end?
At the cable end which is poking out of the box. To sleeve them the sleeve would have to enter into the cable or it just sits on top.
 
Sleeve should be pushed on all the way back to the SWA gland in the bottom of the adaptable box. I've done this myself to terminate SWA sub mains into flimsy plastic CUs that wouldn't take a SWA gland direct.
 
You can't possibly leave it like that aside from looking awful those conductors are not enclosed. No amount of sleeving will make any difference as you will never be able to completely cover them it will always be exposed where they exit the cable. Crimp some 16.0 6181Y within the adaptable box then bring out through a gland.
going to use a large adaptable box . and large trunking . the asethetics are not that important on this occasion as its a garage . i just want to make sure everything is safely carried out to regs .

thanks
 

Reply to SWA too short ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
In the UK, It is said that the neutral wire is connected to ground/earth wire along the way back to the substation. Ive inherited a setup where...
Replies
4
Views
1K
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock