Hi All,

just been to a site with overheating issues - cables showing signs of overheating, shower isolators burning out etc.
I have also noticed some of the 20mm rubber entry grommets in the base of ceiling mounted lights sweating - any one come across this before??? there are actually small droplets of water on the surface of the rubber!!
 
I have come across water droplets in various light fittings before, leaky outside lights, condensation in bathroom lights, water coming in from the after effects of plumbers operating in the void above.
 
I can't imagine how you would go about sweating a rubber grommet?
Sweating a lug onto a cable I can do, and can usually turn my hand to any other metal joining process but rubber?
 
I was up and down ladders at light fittings all day and ended up with a sweaty grommet. Not sure if this helps or not.
 
  • Like
Reactions: 1 person
You can only guess.

Use your imagination times it by ten and you’ll still be miles off target.
 
Is there any tar in the building material around the cables?

Installation was done about 4 years ago, internal corridor with plasterboard ceiling. lamps look to be getting very hot as discolouration of the ballasts etc.

3x light fittings have had issues - 1x cables burnt out at connections 2x failed ballasts (over heated)

bit of a strange one as all cabling is testing out Ok.
 
Are there any hygroscopic materials or any acids used in the location as these can either get stick to things and then absorb enough water to be water droplets or the acid vapour can condense readily as they start reacting with the rubber.
since you have other problems with junctions there may be a corrosive atmosphere.

Other wise it may be there is a hot ceiling (from heating or hot water pipes) and the corridors are cold so the water condenses out as it enters the cold corridor but this would be fairly extreme differentials.
 
Installation was done about 4 years ago, internal corridor with plasterboard ceiling. lamps look to be getting very hot as discolouration of the ballasts etc.

3x light fittings have had issues - 1x cables burnt out at connections 2x failed ballasts (over heated)

bit of a strange one as all cabling is testing out Ok.


Bargain bucket fittings ... cheap crap not fit for purpose.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Sweating rubber grometts
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
chloebear,
Last reply from
Darkwood,
Replies
12
Views
1,418

Advert