Hi All

Quick questions on test results

With Continuity tests i know R1 + R2 results depends on the length of run & size of cable..

When testing it cant be more than a certain figure depending on cable size and breaker size.

How would i know the maximum readings should be? Im guessing on site guide but couldn't find it?

If this is correct do we know a page??

Cheers in advance

Luke
 
pp 100 - 104 red osg. a blind monkey could have found that in less than a minute.
 
Your maximum permitted R1&R2 would theoretically be the maximum permitted Zs of the circuit, minus the external earth fault loop impedance.

So, R1&R2 = Zs - Ze.

However these give you a worst case scenario approach which will not be accurate.

Alternatively, you can obtain the design information to establish the circuit length, then you could more accuraely calculate the expected measured R1&R2 values.
 
So are you looking for calculating Zs or R1&R2?

Your question now appears to make no sense.
 
Hi All

Quick questions on test results

With Continuity tests i know R1 + R2 results depends on the length of run & size of cable..

When testing it cant be more than a certain figure depending on cable size and breaker size.

How would i know the maximum readings should be? Im guessing on site guide but couldn't find it?

If this is correct do we know a page??

Cheers in advance

Luke
Student? If yes Then please state this when asking questions. we do not do students homework on this forum !
Advice if genuine however is free, and if we have given advice do feel free to hit the THANKS button
 
OK, Luke, we are looking to have an EFLI low enough to trip the circuit's MCB/fuse within the BS7671 specified time. ( generally 0.4 secs. for circuits up to 32A.)
this EFLI ( max, ) is found in tables in the bgb, with temperature corrected figures in osg. ( the theory behind this is basically ohms law. the lower the impedance, the larger the fault current. the larger the current, the quicker the MCB/fuse will break ). this figure is Zs. which is composed of Ze + (R1+R2). Zeis obtained either by enquiry or measurement, then when you take that from Zs, you get a max. value for your R1+R2.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Test Results
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
hpmuk,
Last reply from
johndomi12,
Replies
9
Views
1,420

Advert