Evening, has anyone got the current carrying capacity for old Tinned copper cables. Im looking at using an existing cable that looks just under 6mm (Imperial size most likely) for a cooker circuit. IR etc tests out ok. Thanks in advance.....
 
It is probably 7/.044 if it looks 6.0mm which is approximately 6.45mm so theoretically you can use 6.0mm ratings.
 
  • Like
Reactions: Spud28
Evening, has anyone got the current carrying capacity for old Tinned copper cables. Im looking at using an existing cable that looks just under 6mm (Imperial size most likely) for a cooker circuit. IR etc tests out ok. Thanks in advance.....
 

Attachments

It is probably 7/.044 if it looks 6.0mm which is approximately 6.45mm so theoretically you can use 6.0mm ratings.
Thanks for the reply! Is there a chart or table as I would like to confirm on site. Cable definitely looks smaller than 6mm but bigger than 4mm. Cant seem to find any info....!
 
Thanks for the reply! Is there a chart or table as I would like to confirm on site. Cable definitely looks smaller than 6mm but bigger than 4mm. Cant seem to find any info....!
7/036 will be it then, I sent you a chart of sorts, I used that size for 30Amp circuits when I were a Lad, 7/029 was for ring mains as they were known in the past, the very distant past, Telectrix will know all about those cables as well as me and some of the oldies.
 
7/.036 it is, I misread the post as I thought it read larger than 6.0.
 
  • Like
Reactions: Spud28
Brill, thanks a lot - do you have the CCC for this one then please? all I could find is a reference to fuse wire but I cant even find that now!!!
Its on the lists I sent you
 
  • Like
Reactions: Spud28
See Pete's files in #3.
 
  • Like
Reactions: Spud28
  • Like
Reactions: Spud28
copy and file it you never know when might need it again .
 
  • Like
Reactions: Spud28
already done ! Couldn't find the info anywhere, got it after five mins on here, really good!
 
7/036 will be it then, I sent you a chart of sorts, I used that size for 30Amp circuits when I were a Lad, 7/029 was for ring mains as they were known in the past, the very distant past, Telectrix will know all about those cables as well as me and some of the oldies.
It's a joy to see someone asking about tinned cu....so many of them think it's ally, these days.
 
all the young dudes will be asking next about pyro. how does that work. and do they teach them that a collage the old stuff .
 
..... Couldn't find the info anywhere....
At times think "Google" is getting more Dumb,
and ebay more expensive than the local shop !
( Even Alexa wants money )
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Tinned Copper cables ccc
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Spud28,
Last reply from
static zap,
Replies
15
Views
2,388

Advert