Been out to price for another CU change this evening and would appreciate the groups advice.
When looking at the job I noticed that the water bonding is undersized at 4mm on 25mm tails so should be 10mm which is not a problem as I can include that in the quote.
Gas bonding has been done and is 10mm.
The problem I have is when I have gone to look at the main stopcock in the kitchen all the pipework has literally been plastered into the wall so all you can see is the handle of the stopcock. Told the client that I would need to chase the pipework out so I could check and upgrade the bonding accordingly but they would not be keen in this as the kitchen was only redone earlier in the year. The nearest place I could put my bonding without chasing out would be at the kitchen sink which is about 2m away from the stopcock.
How would you all approach this?
Thanks
When looking at the job I noticed that the water bonding is undersized at 4mm on 25mm tails so should be 10mm which is not a problem as I can include that in the quote.
Gas bonding has been done and is 10mm.
The problem I have is when I have gone to look at the main stopcock in the kitchen all the pipework has literally been plastered into the wall so all you can see is the handle of the stopcock. Told the client that I would need to chase the pipework out so I could check and upgrade the bonding accordingly but they would not be keen in this as the kitchen was only redone earlier in the year. The nearest place I could put my bonding without chasing out would be at the kitchen sink which is about 2m away from the stopcock.