Now, I may be barking up the wrong tree, (this had me thinking too..!)
But I think the answer lays in the fact that because there will only be the 1 unfused spur (per socket outlet) then the limiting factor for the single 2.5mm cable is the going to be the 13amp (or smaller) fuses in the appliances being used from that spur.
OSG page 128 gives best current carrying for 2.5 as 27amps... a double socket fed as a spur will be feeding 2 plugs fused at 13amps each, maximum.. or 26 amps total..
So with that worst case scenario.. ie both appliances going full fault, both at the same time, the fuses will go before the capacity for the 2.5 is met.
Obviously, different reference methods give lower capacities, but we are talking about 2 items of electrical equipement faulting at EXACTLY the same time...! so under most circumstances ie single fault, the 13 amp fuse in the plug top gives ample protection.
I know its downstream of the actual change from ring to single cable... but it appears to answer the issue..?
However.... i may be barking in error..