hi guys

hoping you could give me your thoughts,

i am pricing for a consumer unit change, its an old fuseboard with re-wireables.
it has 16mm meter tails, but it has a fairly new looking 100A main fuse.

its a small-ish house..... 2 ring mains, 2 lighting radials, a couple of sockets in the garage, and an immersion heater radial,

i was wondering whether or not i could just down-grade the main fuse to a 60A and keep the existing 16mm tails( no damage, or signs of overheating or burning)
or whether i have to leave the fuse at 100A and fit 25mm tails?

there's no electric shower or oven,

i would appreciate your advice

many thanks
 
as above^^^ it may say 100A on the outside, but be a 60A fuse on the inside. just leave the 16mm tails in, and the fuse is not your responsibility.
 
As #2 & #3 the 16mm tails were probably installed by the DNO along with the fuse, I would be more concerned that the earthing and bonding was correct for the supply characteristics
 
its the dno 100A fuse,
at the moment i am just going on the sticker on the outside, it was late in the evening when i looked at the job, and couldnt pull the fuse to check,

wouldnt it be against the regs to leave the 16mm tails with a 100A fuse?

i just dont want to get any come backs
 
its the dno 100A fuse,
at the moment i am just going on the sticker on the outside, it was late in the evening when i looked at the job, and couldnt pull the fuse to check,

wouldnt it be against the regs to leave the 16mm tails with a 100A fuse?

i just dont want to get any come backs

The OSG pictures assume you are working on a new build....

Do they have 3 electric showers, multiple cookers, a canabis factory in the loft..... The usage for a house is unlikely to rise about 35 amps so I'd leave them welll alone.
 
Hold onto your snips martin,
The requirement for 25mm tails are part of the PME supply regulations so if the supply is PME there is no getting away from that
 
The OSG pictures assume you are working on a new build....

Do they have 3 electric showers, multiple cookers, a canabis factory in the loft..... The usage for a house is unlikely to rise about 35 amps so I'd leave them welll alone.

so, basically, if it does turn out to be a 100A fuse in the holder, it would still be ok to leave the 16mm tails due to a low demand?
 
Yes but you didn't factor in the air fare it cost to go to china and back to get the gear
what it is.....is their `offcuts`...their issued with...lets say a 25 meter drum of tails.....so they put more on a job..than it really was....the rest goes on the bootsale...lol....god, he`s got allsorts..C/Us chuffin RCBOs..drums of twin...lol...
 
Sounds a good bargain, I'm only jokeing around :)
i only get gear at wholesalers as if there's a problem I feel I have a warranty in place
 
OK Martin, With a TNS and a run of less than 2 mtrs you can use 16mm tails as a foot note they normaly fit 80 amp fuses in the DNO for domestic properties nowdays previously they fitted 60 amp
 
the main fuse may be 80-100amp i would upgrade the tails to 25mm the fuse is nothing to do with you but as you are upgrading the system why not upgrade the main tails as its fairly cheap to do so £10 max material , disconnecting them from old board anyway .
i always upgrade to 25mm tails and 16mm earth incoming
 
the main fuse may be 80-100amp i would upgrade the tails to 25mm the fuse is nothing to do with you but as you are upgrading the system why not upgrade the main tails as its fairly cheap to do so £10 max material , disconnecting them from old board anyway .
i always upgrade to 25mm tails and 16mm earth incoming


So do you always cut the seals on the meter then?
 
consumers isolation switch is 30cm max from main fuse murdoch.

if there isnt a isolation point the electricity supplier will gladly fit this for £85 allowing the electrician to carry our his work without cutting seals or pulling fuse.

i could easily re seal using my sealing plyers and SP seals as i am authorised contractor ;)
 
consumers isolation switch is 30cm max from main fuse murdoch.

if there isnt a isolation point the electricity supplier will gladly fit this for £85 allowing the electrician to carry our his work without cutting seals or pulling fuse.

i could easily re seal using my sealing plyers and SP seals as i am authorised contractor ;)

And all your customers are happy to pay this?
 
all my customers appreciate my good quality work,knowledge and professionalism so my advice is golden to them its not much of a hassle to have this done actually can benifit in future , they are there for a reason thats why every new build will have L in and out of switch and nuetral in & out
 
:s every new property has this as standard so copper prices are not the issue , the guys asked for advice put in 25mm and allow for growth of the electrical system
 
:s every new property has this as standard so copper prices are not the issue , the guys asked for advice put in 25mm and allow for growth of the electrical system

Interestingly most products being bought now can be "greener" so when will the time come when we have to rip out 25mm tails and go around fitting 60A fuses!


LOL
 
murdoch needs more than a troll badge ,guys obviously got issues and comes on here looking to see what post he can annoyingly comment on ,
SADDO
 
yeah i agree its a forum ,free speech,etc etc sparks helping other sparks out with varieties of knowledge but some guys are just arrogant ,
the type of guys that sit there self at lunch , that no one likes
 
murdoch needs more than a troll badge ,guys obviously got issues and comes on here looking to see what post he can annoyingly comment on ,
SADDO


For someone with only 52 post and no thanks I think you need to adapt your approach if you're to remain on this forum. Step over the line and the mods will throw you off.

- - - Updated - - -

murdoch needs a troll badge, you troublemaker you lol.

Troll badge - cool!
 
For someone with only 52 post and no thanks I think you need to adapt your approach if you're to remain on this forum. Step over the line and the mods will throw you off.

- - - Updated - - -



Troll badge - cool!
can i taunt him for a bit murdoch......i can 100% guarentee that he wont be back after a taste of my argumentative skills....lol...
 
all my customers appreciate my good quality work,knowledge and professionalism so my advice is golden to them its not much of a hassle to have this done actually can benifit in future , they are there for a reason thats why every new build will have L in and out of switch and nuetral in & out

Which planet are you on?
 
You only NEED 25mm tails is if there is a 100A cut out fuse. Otherwise 16mm will be fine!! It may be prudent to realise that a 100A cut out fuse can only be provided when the Ze/Zs available is adequate to provide clearance times....

I have yet to see a typical standard to large domestic installation come anywhere near drawing a 100A or anything close to it!! Far too many here take more notice of a guidance drawing in the OSG, than using their training and commonsense!!
 
Planet Spongle I think.

What groth of the electrical system, it's a house for gods sake!

Yes a house with no electric shower electric cooker ,pv system outbuilding supplys etc etc etc.

if the fuse is sealed and there is local isolation how do you know what size the fuse is ,only indication it the 100a sticker on cable head fuse.

still cant see the big fuss about fitting 25mm tails while changing a DB

:s
 
Regulations, guidance notes, DNO requirements, actual demand figures, and fuse sizes. To be honest the main reason I upgrade to 25mm tails is for an easy/quiet life.

I could demonstrate by readings and/or calculations that 16mm would be more than adequate. The thing is though, it's easier, cheaper, and quicker just to swap the tails out, so I do. The same goes for 10mm to 16mm main earth and 6mm to 10mm bonding in a lot of cases too.
 
Regulations, guidance notes, DNO requirements, actual demand figures, and fuse sizes. To be honest the main reason I upgrade to 25mm tails is for an easy/quiet life.

I could demonstrate by readings and/or calculations that 16mm would be more than adequate. The thing is though, it's easier, cheaper, and quicker just to swap the tails out, so I do. The same goes for 10mm to 16mm main earth and 6mm to 10mm bonding in a lot of cases too.

my point exactly ,i also upgrade the main earth to 16mm,
no ones said 16mm mains tails isnt adequate but good practice to upgrade while changing DB.
 

Reply to upgrade meter tails, or downgrade main incoming fuse?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Hello, my incoming supply has one main fuse that feeds the next door naghbour it leaves my house to go next door as shown in picture..it's the...
Replies
4
Views
910
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
802
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock