K

Kev2632

Hi,

Why would I be getting very high r1r2 readings and Zs readings in a water heater circuit wired in the existing conduit when the house was built back in 19oatcake...? Would the conduit have anything to do with it and if so? Why?

Thanks
 
Not enough info to make a judgment Kev. What's the earthing system/Ze/Zs readings on other circuits/have you recently installed an RCD etc etc etc
 
All my other circuits readings was good, tn-s system, all connections are tight, and disconnected the water heater supply side from the switch and was still getting weird readings??
 
If it's been wired donkey's years ago I'd be thinking of a JB somewhere.
Is the conduit your CPC?
 
Nope no jb, would the badly made off conduit end or something affect the readings for r1r2 and Zs?
 
A jb could be under a floor, if the conduit is your CPC then a poor loint could be to blame but like Voltz said, I'm clutching a little here
 
kev,
sounds like you have a break in the conduit joint ive had similair problem before in a church :smoking: make sure you completely eliminate the swith from the circuit too
 
Yea that's what I'm thinking too, yea I elminated the switch from the circuit so I only had my live coming in from the consumer unit, and tested to the earth on the backpack where the conduit came in, you know?
 
how high are these readings? I mean that would have to some pretty badly made off conduit.
 
can u uncover any conduit boxes and try pulling on the cables. Surely the benefit of conduit wiring is that it can be rewired easily? May be possible to pull a cpc in?
 
with the CSA of the conduit in which its wired, will that allow it too have such a high reading? or would that normally give a very low reading if the conduit is " sound", because the CSA area is bigger so it should in theory have alot lower reading than the R1+R2 of live to earth in twin and earth yea??
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Very high r1+r2 readings and Zs in conduit?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
25

Advert

Thread statistics

Created
Kev2632,
Last reply from
VoltzElectrical,
Replies
25
Views
3,961

Advert