About 20 years ago I bought an old table saw from a local school. I only had single phase at the time so I changed the motor and switchgear as it was 450V. I'm thinking of buying a 3 phase 50s bandsaw and have the same problem, but I can't remember how to work out the size of the replacement single phase motor. Are there likely to be any other problems?
 
I would have thought the easiest way round the issue is to match the new motor to the one you take off. I.E the same h.p / kw rating and the same speed as the three phase one you take off
 
Why not use a VFD and keep the three phase motor?
 
Interesting idea, I guess these days a VFD is probably cheaper than a new motor? Also you probably get soft-start and the speed control might prove useful.
 
I would have thought the easiest way round the issue is to match the new motor to the one you take off. I.E the same h.p / kw rating and the same speed as the three phase one you take off
This is all the info I have.
 

Attachments

  • What do I need to know to calculate size of single phase motor? sega motor plate - EletriciansForums.net
    sega motor plate.jpg
    109.1 KB · Views: 28
I am/was assuming changing the motor will be the most economical route at the moment.
VFDs are dirt cheap and will save the hassle of trying to find the right frame to fit your machine.
 
This is all the info I have.
Can't read that, but how old is the motor? A VFD will put a lot more stress on the motor windings and an old motor with old insulation will not like it.

Note also that a VFD running from a single phase supply provides 230VAC 3 phase not 415, at 50Hz. Which is fine if your motor is wound and can be connected accordingly.

Edit...can read it now....you can connect in delta 250V so the VFD voltage level should work. I would be concerned about the winding insulation with VFD operation.
 
Can't read that, but how old is the motor? A VFD will put a lot more stress on the motor windings and an old motor with old insulation will not like it.

Note also that a VFD running from a single phase supply provides 230VAC 3 phase not 415, at 50Hz. Which is fine if your motor is wound and can be connected accordingly.

Edit...can read it now....you can connect in delta 250V so the VFD voltage level should work. I would be concerned about the winding insulation with VFD operation.From what I'm told the machine is 50s or 60's.
From what I have been told the machine could be 50's or 60's. Is it possible to estimate the HP or KW from the info on that plate?
 
It's around 1.5HP - if you are using the 260V line the "power" it will consume is around 260 x 5 x 1.73 = 2.25kW (not quite right it's actually VA, but let's keep it simple),

However not all this power is converted to output, so it is normal to take around 60% of this on newer motors and 50-55% on older motors (the "loss" is efficiency and power factor) - giving an output around 1.125kW (then divide by 0.746 to convert to hp) = 1.5HP

Difficulty to actually say as a more efficient motor could give up to 1.8hp output, one less down to 1hp.

This motor could be wired in delta for a 260V voltage, that should be ok for a VFD at 230V from a 230v single phase supply.

Try somewhere like Newton Tesla | Mitsubishi Electric Products, Motors & Gearboxes (newton-tesla.co.uk) if you speak to them they would advise if the motor is suitable.
 
It's around 1.5HP - if you are using the 260V line the "power" it will consume is around 260 x 5 x 1.73 = 2.25kW (not quite right it's actually VA, but let's keep it simple),

However not all this power is converted to output, so it is normal to take around 60% of this on newer motors and 50-55% on older motors (the "loss" is efficiency and power factor) - giving an output around 1.125kW (then divide by 0.746 to convert to hp) = 1.5HP

Difficulty to actually say as a more efficient motor could give up to 1.8hp output, one less down to 1hp.

This motor could be wired in delta for a 260V voltage, that should be ok for a VFD at 230V from a 230v single phase supply.

Try somewhere like Newton Tesla | Mitsubishi Electric Products, Motors & Gearboxes (newton-tesla.co.uk) if you speak to them they would advise if the motor is suitable.
Now I know why I got a E in A level physics. Thank you.
 
i only got a B.... i spelt my name wrong on the exam paper.
 
Why is a VFD considered the best option? Apart from the possible difficulty of finding a single phase motor with similar mountings, would it not be simpler to put in a single phase 1.5kW? Is it just price?
I suppose other considerations are that it would be better to have a breaked motor or the bandsaw might continue turning for minutes when switched off and the possible need for soft start. I guess this is something a VFD allows?
I have no idea of quality but shouldn't I be able to buy a single phase motor for around £200? Surely a VFD and paying someone to wire it is going to cost more?
 
Why is a VFD considered the best option? Apart from the possible difficulty of finding a single phase motor with similar mountings, would it not be simpler to put in a single phase 1.5kW? Is it just price?
I suppose other considerations are that it would be better to have a breaked motor or the bandsaw might continue turning for minutes when switched off and the possible need for soft start. I guess this is something a VFD allows?
I have no idea of quality but shouldn't I be able to buy a single phase motor for around £200? Surely a VFD and paying someone to wire it is going to cost more?
Well a 2kw vfd will cost around £55 off ebay or similar.

It can provide adjustable speed control without having to shift belts in pulleys etc.

It can also soft start to reduce the impact both mechanically and electrically plus a few other advantages.

One other advantage is that to a greater or lesser extent the existing switchgear can remain in place, often when moving to single phase most of the switchgear needs to change.

One other alternative is to use a rotary converter, this takes 230V input and produces a 415V three phase output, you can then use this for multiple machines which then don't require modifications.

My husband uses this to drive his lathe or milling machine, or surface grinder all of which are as they were designed, no mods
 
Well a 2kw vfd will cost around £55 off ebay or similar.

It can provide adjustable speed control without having to shift belts in pulleys etc.

It can also soft start to reduce the impact both mechanically and electrically plus a few other advantages.

One other advantage is that to a greater or lesser extent the existing switchgear can remain in place, often when moving to single phase most of the switchgear needs to change.

One other alternative is to use a rotary converter, this takes 230V input and produces a 415V three phase output, you can then use this for multiple machines which then don't require modifications.

My husband uses this to drive his lathe or milling machine, or surface grinder all of which are as they were designed, no mods
Thank you. I thought a quality VFD would cost more. I guess £55 is a budget version? Do I assume from your earlier post that the wiring to the motor, you mentioned 260, would also have to be changed with a VFD? I don't understand star and delta wiring but looking at the the plate I have shown this motor can be wired either way? The machine currently has a 3 phase plug.
 
Thank you. I thought a quality VFD would cost more. I guess £55 is a budget version? Do I assume from your earlier post that the wiring to the motor, you mentioned 260, would also have to be changed with a VFD? I don't understand star and delta wiring but looking at the the plate I have shown this motor can be wired either way? The machine currently has a 3 phase plug.
I would expect the 260V motor would be ok for 230V supply as is.

Basically a three phase motor has three windings, you can connect three windings like a star - the three supply phases to each of the windings, with all the other ends of the windings connected to a common point, or as a delta - winding 1 between supply phase 1, and phase 2, winding 2 between phase 2 and phase 3, and winding 3 between phase 3 and phase 1 - there will be a connection diagram in the motor terminal housing or somewhere similar.

Yes £55 Would be a cheap and cheerful version.
 
From what I have been told the machine could be 50's or 60's. Is it possible to estimate the HP or KW from the info on that plate?
If a vfd is any use I have a eurotherm 650 single phase inverter. As new still boxed.
Input 220-240v AC 10.5A, 1or 3 phase
Output 220-240v. 4A 3 phase
£50.00 postage £5.00
 
If a vfd is any use I have a eurotherm 650 single phase inverter. As new still boxed.
Input 220-240v AC 10.5A, 1or 3 phase
Output 220-240v. 4A 3 phase
£50.00 postage £5.00
I think it may be a tad small. I think I need 5A output. But to be honest I don't really know enough to be sure.
 

Reply to What do I need to know to calculate size of single phase motor? in the Electrical Engineering Chat area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock