Opening an external lighting joint box.
Ahh, good old water powered lights. Always remember to drill a hole in the bottom of the box. If the water can’t flow the lights won’t work!
 

MJPD29

-
Esteemed
Arms
Reaction score
3,043
Shop in Dublin had refurb carried out end of last summer. New 35mm tails connected into old panel. Clearly someone didn't check their final connections. The same idiot also managed to break nearly every single cover on the terminals across every panel.
 

Attachments

  • When electrics go wrong!!! 20210705_082550 - EletriciansForums.net
    20210705_082550.jpg
    369.2 KB · Views: 135
  • When electrics go wrong!!! 20210705_082421 - EletriciansForums.net
    20210705_082421.jpg
    341 KB · Views: 170
Reaction score
18
Call out to loss of power on house ring main, further conversation with owner , they had various sockets lowered from switch height to low level downstairs only a month back by a electrician, said electrician as been back to find the cause but had to leave without solving issue. Although he did disconnect the live and neutrals from fuse board so he got some power back on . That was 3 weeks ago. Said Rfc controls the combi so no heating/hot water and extension leads to various rooms to keep going.
After few tests got open circuit on neutrals and neutral live earth faults. After a bit of bashing nice new painted and fresh plastered walls where the old sockets used to be .Found 4 joints in wall in wagos taped up behind channel. One burnt out giving me the short and another poor joint giving me the open circuit. Ko boxes fitted and blank plates over top new joints.
 

Attachments

  • When electrics go wrong!!! IMG_0281.JPG - EletriciansForums.net
    IMG_0281.JPG
    429.5 KB · Views: 117
  • When electrics go wrong!!! IMG_0282.JPG - EletriciansForums.net
    IMG_0282.JPG
    422.9 KB · Views: 106
  • When electrics go wrong!!! IMG_0283.JPG - EletriciansForums.net
    IMG_0283.JPG
    370.6 KB · Views: 115

Simon47

-
Esteemed
Arms
Supporter
Reaction score
1,160
Could be worse, could be all metal conduit, threaded into the fittings, and needing half a mile* of other stuff removing before you get back to that one. Of course, I'm guessing they've used male adapters rather than female adapters with bushes.

* Exaggerated for effect.
 

timhoward

-
Esteemed
Arms
Reaction score
8,231
Could be worse, could be all metal conduit, threaded into the fittings, and needing half a mile* of other stuff removing before you get back to that one. Of course, I'm guessing they've used male adapters rather than female adapters with bushes.

* Exaggerated for effect.
In this case it's male adaptors with lock rings both sides and there's another 5 of these fittings 2m apart probably all connected the same way, with singles for another lighting circuit running uninterrupted through all of it....
But yes, at least it isn't galv....!
 

freddo

-
Esteemed
Arms
Supporter
Reaction score
4,531
Lucky. We were recently working on an installation in PVC conduit, no adaptors used, just a plastic lock ring glued on to the conduit either side of the boxes/trunking. :(
 

nicebutdim

-
Esteemed
Arms
Reaction score
6,059
In this case it's male adaptors with lock rings both sides and there's another 5 of these fittings 2m apart probably all connected the same way, with singles for another lighting circuit running uninterrupted through all of it....
But yes, at least it isn't galv....!

Male pvc adapters are terrible. Badly designed with terrible lock rings and, for the most part, much less practical than their female counterparts. I dislike them intensely.
 

pirate

-
Esteemed
Arms
Supporter
Reaction score
5,323
A Scottish thing!
Plus my original post didn't have enough "characters" so i added Mickey...
Humour makes the day go better!
 

crr003

DIY
Reaction score
4
May I add this one (I had the offending sink waste disposal replaced by a plumber but I kept the old one).

When electrics go wrong!!! IMG_6979 - EletriciansForums.net

There was a big bang and a breaker tripped. The tenant found this blackened socket. Where did all this black deposit come from? The molded plug looks undamaged - the 13A fuse was fine - can anyone explain what physically blew up here? I'm just interested.
I plugged the unit into an extension cable in the back garden and it blew the fuse in the extension cable (and left the same black deposit). The disposal was free to rotate so I don't know where the problem was.
 

littlespark

-
Esteemed
Arms
Reaction score
16,356
May I add this one (I had the offending sink waste disposal replaced by a plumber but I kept the old one).

View attachment 97391

There was a big bang and a breaker tripped. The tenant found this blackened socket. Where did all this black deposit come from? The molded plug looks undamaged - the 13A fuse was fine - can anyone explain what physically blew up here? I'm just interested.
I plugged the unit into an extension cable in the back garden and it blew the fuse in the extension cable (and left the same black deposit). The disposal was free to rotate so I don't know where the problem was.
Classic dead short between live-neutral or live-earth. The fault is nothing to do with the motor, so its spinning freely.

The black deposit is powdered charred metal. If you can visually inspect the plug pins with a good plug, youll see damage on the pins. The metal has laterally exploded into powder. If not the pins, then the socket youre plugging into.

Best place for that appliance now is the council dump.
 

crr003

DIY
Reaction score
4
Classic dead short between live-neutral or live-earth. The fault is nothing to do with the motor, so its spinning freely.

The black deposit is powdered charred metal. If you can visually inspect the plug pins with a good plug, youll see damage on the pins. The metal has laterally exploded into powder. If not the pins, then the socket youre plugging into.

Best place for that appliance now is the council dump.
Thanks for replying.

I had a look at the plug pins before I threw it all out - they looked ok which confused me (easily done...). I was hoping to see the black insulation that covers about half of the pin vaporised, but it looked OK. Although the 13A fuse was intact (electrically/physically), the "live end" connector in the plug that holds the fuse was much blacker than the other end. I thought the fuse should have protected something, but it looks like the short was somehow before the fuse. The disposal had been working OK for about 8 years and then "bang"!
 

Simon47

-
Esteemed
Arms
Supporter
Reaction score
1,160
My guess would be that a build up of dirt and damp eventually created a track which allowed an arc to form. Normally the distance is such that even when there's lightning induces surges about, you won't get arcing between L & N. But add dirt and moisture, and perhaps something sub-standard in manufacture, and you can get arcing. Once an arc forms, then the ionised air is a good conductor and the arc won't go out until either the power is cut off (the upstream fuse/breaker goes) or the arc is manipulated in such a manner that it gets broken. The energy in the arc can be "a surprising amount", and in all that black there is likely to be as least some it conductive material - so I'd be replacing the socket as well because it definitely doesn't have the arc resistance that it once had.
 

crr003

DIY
Reaction score
4
My guess would be that a build up of dirt and damp eventually created a track which allowed an arc to form. Normally the distance is such that even when there's lightning induces surges about, you won't get arcing between L & N. But add dirt and moisture, and perhaps something sub-standard in manufacture, and you can get arcing. Once an arc forms, then the ionised air is a good conductor and the arc won't go out until either the power is cut off (the upstream fuse/breaker goes) or the arc is manipulated in such a manner that it gets broken. The energy in the arc can be "a surprising amount", and in all that black there is likely to be as least some it conductive material - so I'd be replacing the socket as well because it definitely doesn't have the arc resistance that it once had.
Thanks.
The socket is under a sink and although there was no sign of damp/leaks it could have got wet. I'm annoyed I didn't measure L-E resistance etc. of the disposal when I had the chance.
Here's another picture of the extension block I plugged the disposal in to see what would happen - note the burned groove to the left of the N hole and the edge of the extension is burned off and there's a nice image of where the fuse holder fits! (Fuse didn't blow). Powerful stuff.

When electrics go wrong!!! IMG_0196 - EletriciansForums.net
 

Biff61

-
Reaction score
30
When electrics go wrong!!! MRV2 - EletriciansForums.net When electrics go wrong!!! MRV2 - EletriciansForums.net
here's the result of a numpty damaging a brand new voltage stabilizer by getting the 3 phase connections on a generator wrong, and its all marked R,S,T,N. Connected a phase output line to the neutral and neutral to a pahse so it put two phases through the master rotavolt controller and left the incoming utility switched on while testing the changeover. By the time a replacement is shipped from UK looking at around 5K. Also took out the 400amp Auto changeover switch, another 3k to replace. Lucky not to lose the generator as well as it shut down within about 5 seconds of power being turned on. Thankfully the main switch in the MDB was off it could have run in to hundreds of thousands to repalce printers, photocopiers, and the data centre.
Lets just say he's not working for us anymore and will not be getting references.
 
Reaction score
148
When electrics go wrong!!! IMG_2511 edited - EletriciansForums.net When electrics go wrong!!! IMG_2511 edited - EletriciansForums.net
Thought I would share this burnt-out Inverter that I discovered. The customer wondered why it had stopped generating!
This was caused by water ingress & water pooling in the bottom causing a short between the grid connection 3 phases & which must have short-circuited the DC MC4 input before finally giving up. Good ole Samil Inverter 17kw 3 phase, no wonder they went bust. (Chinese) . I think I am going to give Rayliegh Instruments a try from CEF, I would prefer Fronious but there is a back order, due in sept maybe.
 

Doomed

-
Esteemed
Arms
Reaction score
685
Had been running like this for 3 years - we got called in as they never got a cert off the original electrician and he told them to stop pestering him a few months back.
When put back correctly we found many isues that caused the RCD's to trip - shared neutrals, pinched neutral to back box in two seperate postions, switch fuse spur with neutral and earth swapped.
 

Simon47

-
Esteemed
Arms
Supporter
Reaction score
1,160
Saw a safety alert recently in a large engineering business. Someone was doing some gouging*, cable was a bit short to reach where he was working, and it seems the cable wasn't secure in the trailing socket. Socket comes off leaving exposed wire ends which then falls ...
... onto the gas axe (oxy-acetylene cutting torch) he was also using on the job.
The ensuing arcing from the gouging supply cut the gas axe in half - luckily in the bit between valves and torch head. Had it dropped on the valves then it would have released copious quantities of oxygen and/or acetylene in the presence of a 'kin big arc.

What I did find interesting was that the alert didn't mention the fact that the socket shouldn't have come off the cable - only to pull the cable by the cable rather than the connector.

* For those who haven't seen it, gouging involves striking up a 'kin big arc (very much like arc welding) to melt the metal, and using a jet of compressed air to blow the molten metal out. It's a very effective way of cutting thick steel - though to say it lacks finesse would be an understatement. Example
 

oscar21

Esteemed
Reaction score
327
This definitely went wrong for my mate yesterday. He got a call out for an RCD tripping in a shop so went to have a look, managed to fix that fairly quickly and whilst he was there they said can you have a look at our lights so he did. It was a grid ceiling with 600x600 LED panels in, and the way they were wired was with a plug/socket type affair on short leads and T-pieces. The name of the plug escapes me for now but its a flat 3 pin plug same as these.

When electrics go wrong!!! IMG_20231013_173907_446 - EletriciansForums.net

You can get short leads with a male plug on one end and a female socket on the other you then use 3/4/5/etc way splitters like above to give you ways for the lights which obviously have a male plug fitted. We fitted loads of them the other year on shop refits, I didn't like them as you couldn't really support the cables between the lights and they just ended up on top of the grid, also they were really hard to push together and engage the clips and sometimes if you pulled them apart it broke the T-splitter instead exposing the pins.

Anyway, some of the lights weren't working (not one of our jobs by the way) so he goes into the grid ceiling to have a look, grabs one of the leads at a junction and gets a big electric shock, falls off the ladders, cuts his leg and twists his knee quite badly. Turns out that the T piece had melted and exposed the connection, probably because it was never fully pushed together. He's been to A&E today and they said he has probably damaged his ligaments.

So not too sure who is at fault really, I suppose by the book he should have turned the power off, locked the MCB off and got the barriers out, tested dead etc etc but when you are fault finding like that you really need to do it live in order to find where the live bit ends and the fault begins, which he certainly did do yesterday. Or is the shop at fault for letting someone near their dangerous electrics? I'm not too sure how the shock was that bad but he reckons he thought his number was up and can't remember falling off the ladders, just getting up off the floor. He was on fibreglass steps, boots and carpet so it wasn't that, must have been the ceiling grid that was earthed, either that or it just wen't between the pins in the plug via his hand and he was being over dramatic about the shock to justify falling off the ladders.
 

Reply to When electrics go wrong!!! in the Electrical Forum area at ElectriciansForums.net

Similar Threads

I could imagine the CMOS Bios Battery circuits are quite similar on all recent mainboards. What does it look like and how does it work...
Replies
3
Views
2K
So I just got let go from my job last week as operations manager was in the role for 6 months, previously I was a transport supervisor at...
Replies
20
Views
3K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
T
First post but been reading all your fantastic threads for a while though ;) I'm looking to get into the trade proper after being in and out a...
Replies
10
Views
1K
K

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top