Been called out today to a smell of burning from a consumer unit.
On investigation busbar terminal on RCD found to be burnt out (looks like the busbar was either loose or missed the terminal to start with)
There were no other issues with the install (dual rcd board etc) apart from the cu being plastic and last eicr expired in 2014.
My question is having replaced one of the RCD's what sort of certificate would you issue? neither an EIC or MWIC seem appropriate as it is not a circuit as such.
I have put all the test results, trip times, Zs etc on my invoice so there is a record of them and will be going back in the new year to complete a full eicr for the customer but curious to know what you would all issue.
Have a good Christmas and New Year everyone.
Reactions: FatAlan
minor new works, as a repair.
Which certificate?
PJH2903,
Strima,