Hi,
With a "granny" charge point, you can just have an extension socket going from your indoor house plug mains and charge your vehicle like that.

But if you have a 16A + charger then you need a expensive type B RCD to be installed....which has DC 6mA and 30mA imbalance detection.

Why the difference?.....why no RCD needed with the granny charger?

"granny" charger <10A
 
Hi,
With a "granny" charge point, you can just have an extension socket going from your indoor house plug mains and charge your vehicle like that.

But if you have a 16A + charger then you need a expensive type B RCD to be installed....which has DC 6mA and 30mA imbalance detection.

Why the difference?.....why no RCD needed with the granny charger?

"granny" charger <10A


It does, because all socket outlets require RCD protection in any case.

Also you should dedicate a particular outlet for this purpose, and select a suitable RCD for the type of load.
 
  • Like
Reactions: treezleef
It does, because all socket outlets require RCD protection in any case.
Thanks, but i think a household RCD cant detect the >6mA of DC?

A >16A EV charger needs to be protected by an RCD which can detect >6mA of DC...(and not be blinded by it)
Why does this apply to 16A chargers, but not to 10A chargers?
 
It does, because all socket outlets require RCD protection in any case.

Also you should dedicate a particular outlet for this purpose, and select a suitable RCD for the type of load.
Not necessarily all socket outlets.
 
  • Like
Reactions: treezleef
  • Like
Reactions: treezleef
Thanks, but i think a household RCD cant detect the >6mA of DC?

A >16A EV charger needs to be protected by an RCD which can detect >6mA of DC...(and not be blinded by it)
Why does this apply to 16A chargers, but not to 10A chargers?

It doesn't have to, the rcd only detects an unbalance between phase and neutral (or all phases and neutral) by their very design no rcd operates on dc itself.

They need to not be blinded by the dc and the charge point itself needs a device that detects >6mA DC. These are two seperate functions as the rcd operates on unbalance whilst the detection of dc is not necessarily unbalanced
 
  • Like
Reactions: treezleef
They need to not be blinded by the dc and the charge point itself needs a device that detects >6mA DC.
..Thanks, yes , a 16A charge point needs a device that detects >6mA DC....the thing is, if you use a 10A granny charger, then you dont have any device in the path that detects the >6mA DC...so why do 16A charge points need to detect >6mA DC?
These are two seperate functions as the rcd operates on unbalance whilst the detection of dc is not necessarily unbalanced
Thanks, but the thing is, that the device that detects unbalance, and the device that detects DC, is the same device, its a "fluxhgate based current sensor"....at least, this is the case in a 16A chargepoint.

The mystery is why detection of DC leakage is not necessary in a granny charger?
 
Thanks, why does the granny charger not need to have detection of DC leakage?
(woops sorry, my above post suddenly re-appeared)
 
Which 13a outlets don't in a home?

The op was talking about 13a outlet to a granny charger
Ah but you quoted all socket outlets.
 
  • Like
Reactions: treezleef
..Thanks, yes , a 16A charge point needs a device that detects >6mA DC....the thing is, if you use a 10A granny charger, then you dont have any device in the path that detects the >6mA DC...so why do 16A charge points need to detect >6mA DC?

Thanks, but the thing is, that the device that detects unbalance, and the device that detects DC, is the same device, its a "fluxhgate based current sensor"....at least, this is the case in a 16A chargepoint.

The mystery is why detection of DC leakage is not necessary in a granny charger?
Probably because it is both considered a small power, and is a legacy design.

I don't think they should be allowed tbh because they don't have the proper protection range applicable to a genuine charge point.

The design of all charge points is down to the individual manufacturers, sure some may use a combined device, but many, in fact the majority at the moment do not.
 
  • Like
Reactions: treezleef
Ah but you quoted all socket outlets.
In relation to a post about a specific device which plugs into a 13A socket outlet!!

Re-word it if you want

"All socket outlets, in relation to this question, relating to but not exclusive to the device that may or may not be used within that outlet, in respect of the current range identified within this question, located within or associated with the property or properties associated with this question, must have rcd protection "

If you don't believe it is rather obvious to anyone reading this thread.
 
Probably because it is both considered a small power, and is a legacy design.
Thanks for confirming that a granny charge point (10A) doesnt need a ">6mA DC detection".

To my mind, this is a little non-sensical, as the voltage is just the same, and the danger to human life is just the same. Would you agree?

It really does make you wonder why the ">6mA" detection has been mandated for 16A chargers?

...or why it hasnt been mandated for the granny chargers?
 
A 'granny cable' or more correctly a Mode 2 charging cable will incorporate an In-cable Control Box (ICCB) that has RCD functionality.
 
  • Like
Reactions: treezleef
Thanks for confirming that a granny charge point (10A) doesnt need a ">6mA DC detection".

To my mind, this is a little non-sensical, as the voltage is just the same, and the danger to human life is just the same. Would you agree?

It really does make you wonder why the ">6mA" detection has been mandated for 16A chargers?

...or why it hasnt been mandated for the granny chargers?
No, I wouldn't agree, the backfeed of 6mA is not related to voltage, but to the current being rectified in the vehicle.

As you increase the current there is a potential corresponding increase of dc component being backfed; so say a malfunctioning rectifier circuit introduces 0.04% dc - with a 10A charger this is 4mA this is below the limit for B type rcd, so a suitable Rcd would still operate if there were a fault. However if you have a 16A charger, then .04% would give 6.4mA - this is above the allowed value for the rcd, therefore it may become blocked, it is therefore necessary to either provide an Rcd which will continue to work with dc much greater than this, or provide additional protection that operates if the dc component is larger than that which could be acceptable to the rcd.

Basically you need to ensure a rcd will operate if there is an earth fault, or if you cannot, you must disconnect the circuit in case there is an earth fault as the rcd protection wouldn't be guaranteed.
 
  • Like
Reactions: loz2754
As you increase the current there is a potential corresponding increase of dc component being backfed

Thanks..
Though According to the following, the cause of DC leakage with EV's is insulation failure, coupled with the fact that there is a large DC battery in the EV...

It says nothing about DC leakage currents being more likely, the higher is the charge current...


...so from the above, you would again have to ask, why dont granny chargers, that charge at 10A, need a DC leakage detection for >6mA DC leakage?
 
Last edited:
Thanks..
Though According to the following, the cause of DC leakage with EV's is insulation failure, coupled with the fact that there is a large DC battery in the EV...

It says nothing about DC leakage currents being more likely, the higher is the charge current...


...so from the above, you would again have to ask, why dont granny chargers, that charge at 10A, need a DC leakage detection for >6mA DC leakage?

Well any electronic conversion of ac to dc will introduce harmonics back into the system due to the nonlinearity of the electronic rectifier - although dc is not strictly an harmonic it will be introduced, and you could do a Fourier analysis to calculate it.
 
  • Like
Reactions: treezleef
Well any electronic conversion of ac to dc will introduce harmonics back into the system due to the nonlinearity of the electronic rectifier - although dc is not strictly an harmonic it will be introduced, and you could do a Fourier analysis to calculate it.
Thanks, but that isnt the cause of the ">6mA DC leakage " that needs to be detected by the 16A EV chargers.

Also, the harmonics from SMPS's doesnt put any DC into the mains.

The >6mA DC leakage is due to insulation failure, and this is just as likely with a 10A charger as with a 16A charger, so why do 10A chargers not need ">6mA DC leakage detection"?
 
surely the need for a RCD or not is dependent on granny's last will and testament. no point in electrocuting her if you're not included.
 
We used to chuck grannies off buses. But we’ve been told not to as she’s our “mammies mammy”
 
...so from the above, you would again have to ask, why dont granny chargers, that charge at 10A, need a DC leakage detection for >6mA DC leakage?
You need to re-read post #13...
 
  • Like
Reactions: treezleef
You need to re-read post #13...
A 'granny cable' or more correctly a Mode 2 charging cable will incorporate an In-cable Control Box (ICCB) that has RCD functionality.
thanks yes, but a granny charger does not have an RCD which is capable of measuring >6mA DC.
 
Good quality and new 'granny chargers' should have rcd protection of some sort built into them now.
seen some awful chinese ones that didnt have it mind. use at your own risk sort of stuff.
 
  • Like
Reactions: treezleef

..theabove video prooves that the granny chargers contain no ">6mA DC leakage" detection or protection.
So it seems surprising that EV chargers have to have it.
 
thanks yes, but a granny charger does not have an RCD which is capable of measuring >6mA DC.
From Jan 2018 a Mode 2 cable ('granny cable') manufactured to BS EN62572 had to have >6mA DC fault protection.

btw... it's not a 'granny charger' it just supplies 230AC to the on-board charger.
 

..theabove video prooves that the granny chargers contain no ">6mA DC leakage" detection or protection.
So it seems surprising that EV chargers have to have it.
No, it is probably legacy that these rubbish granny chargers do not.

Rcd and dc leakage are two seperate functions, they may be within the one device, in which case it is no longer an rcd it is a combined device.

You have to provide suitable protection on all equipment to disconnect in the case of a fault, ADS is not always sufficient, in which case RCD or equivalent protection is required. If you cannot rely on a standard RCD then you either need a special RCD or additional protection to disconnect.

It isn't a difficult concept.
 
From Jan 2018 a Mode 2 cable ('granny cable') manufactured to BS EN62572 had to have >6mA DC fault protection.

btw... it's not a 'granny charger' it just supplies 230AC to the on-board charger.
Thanks,from 7:40 onwards, the efix experts are saying that "granny charge points" dont have ability to detect the >6mA DC. This video is from 2021....

 
Thanks,from 7:40 onwards, the efix experts are saying that "granny charge points" dont have ability to detect the >6mA DC. This video is from 2021....

I have an old landrover from 1980, and that doesn't have the latest emissions limit introduced in 2018.

Why is it that the landrover group doesn't have to meet the emissions limits like other car manufacturers???
 
  • Like
Reactions: treezleef
Thanks, but it seems different.....car emissions is bad, but electric shock (so they say), is instant death. ...or so they say...(incidentally, having taken many full 240VAC mains across the chest, often with my pectoral muscles vibrating at 50Hz...i dont believe leccy is as bad as they say, but thats just me.)
The "powers" say that leccy is deadly....instantly so....so it seems odd that old granny charge points arent banned.
I have no idea how we can check if granny charge points do need >6mA detection, because most like me cant afford the standards.
 
  • Dislike
Reactions: DPG
Thanks, but it seems different.....emissions is bad, but electric shock (so they say), is instant death. ...or so they say...having taken many full 240VAC mains across the chest, often with my pectoral muscles vibrating at 50Hz...i dont believe leccy is as bad as they say, but thats just me.
The "powers" say that leccy is deadly....instantly so.

Plenty of people might disagree if they weren't already dead from electrocution.
 
  • Like
Reactions: DPG and Julie.
Thanks, but it seems different.....car emissions is bad, but electric shock (so they say), is instant death. ...or so they say...(incidentally, having taken many full 240VAC mains across the chest, often with my pectoral muscles vibrating at 50Hz...i dont believe leccy is as bad as they say, but thats just me.)
The "powers" say that leccy is deadly....instantly so....so it seems odd that old granny charge points arent banned.
I have no idea how we can check if granny charge points do need >6mA detection, because most like me cant afford the standards.

Dangerous attitude. Electricity can, and does, kill.
 
  • Like
Reactions: nicebutdim
What about "granny chargers" on TN-C-S supplies, This could possibly pose a large shock risk. (iv pulled the pin out of the grenade)

But as reg 722.411.4.1 says any outlet which is likely to be used to charge a car cannot use a PME earth without other precautions

And as mentioned previously BS EN62572 means >6mA DC fault protection has to be included in the granny charger

So if using quality items on a decent electrical installation, then there should be no risks


But you will always be able to buy a cheap crap granny charger straight from china, and plug it into a non RCD socket circuit in a house in which the fixed wiring could do with TLC and has not been inspected since it was installed 50 years ago

I mean you can order the so called "suicide showers" to the UK from china, kind of says it all
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
southampton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Why does a "granny" charger for EV (<10A) not need an RCD?
Prefix
N/A
Forum
Electric Vehicles Advice Forum
Start date
Last reply date
Replies
30

Thread Tags

Advert

Thread statistics

Created
treezleef,
Last reply from
marcuswareham,
Replies
30
Views
10,334

Advert