Discuss Will a 14.5kw oven work on a 32 amp connection? in the UK Electrical Forum area at ElectriciansForums.net
Hi I have been having problems with my cooker and want to change it.
I have looked at several that say a 32amp permanent connection is required, which is what I have, however, I don't think the specifications sheet is correct.
An example is 14.5kw cooker should be on a 32 amp connection. This does not seem right to me as 14500/240 = 60.4amps.
I have looked at a few and the spec sheets are similar - e.g.....
If I were to use all elements together (e.g. Xmas lunch) am I likely to have problems?
Thanks.
No, it will actually be fine.
The only time the cooker would would draw maximum power is if you turn all elements on together exactly at the same time and they are all heating up to the prescribed temperature together. That rarely happens in real life. Even if you did, a B32 circuit breaker wouldn't trip at 60 amps unless the current draw persisted for about 2 minutes, and some elements will have reached temperature by then.
Once an element reaches temperature it stops drawing power until it falls in temperature enough to warrant heating up again, so the current draw in practise would be a lot lower.
Provided the circuit is fully rated for 32A (so typically at least 6mm cable) it will be fine as described above.
For a domestic cooker the standard allowance is 10A plus 30% of the remainder, and 5A more if a kettle socket is present.
14.5kW = 63A at 230V so requirement would be 10A + 30% (63A - 10A) + 5A = 30.9A so within a 32A circuit.
Reply to Will a 14.5kw oven work on a 32 amp connection? in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Hi, I've searched these forums and have found quite a bit of good information, but not specifically to my query. My house is about 9 years old...