I understand where you are coming from but the question is about codeing for lack of RCD protection to a socket outlet. I'll refer you to the reg I quoted which makes no distinction on socket type....only that the rating is 20a or less. Which means that in order not to code a 2/5a socket must either have rcd protection,or be specifically labelled. You are assuming that DIY dave will know that a 2/5a socket is only for a table lamp,thats an assumption too far.
I see your point but its all open to interpretation!
Note b of the reg you have quoted (411.3.3) states that the socket does not have to be RCD protected if its 'provided for connection of a particular item of equipment' - which the 2A/5A plug does, to my mind.
Obviously some muppet could change a 13A socket to a 2/5A socket but anyone with a screwdriver can do want he wants. All I say is let them suffer the consequences!
IIRC 16th only required RCD protection for sockets where the equipment was likely to be used outside, which would exclude sockets specifically intended for lighting indoors, so I would agree with a C3.
I've given my thoughts on 2/5A lighting sockets and got shot down in flames, so does anyone have any better ideas for keeping installations safe?
There's nothing to stop a 2/5a plug being put on any other item of equipment though. you cant assume that such a plug will only be used on a table light,there are plenty of people who would be daft enough to stick a 5a plug on their hair dryer if that was the most convenient socket!
My point was more to the fact that the regs trys to protect anyone that doesn't have a tool (eg. screwdriver). Anyone with a toolbox can do anything they want, not just change 13A plugs to 2/5A plugs. It just can't legislate for the morons with a screwdriver! In which case they deserve all they get!
Yes they should be....411.3.3. But if they complied at the time of installation and are not likely to supply equipment outdoors....(clearly not) then code 3.
If you lablel them as specifically for table lamps then no code at all IMO 411.3.3 (b)
Recently I got called out to a similar install with 13a sockets instead of 2/5a's. During a dinner party they'd plugged in a 2kw fan heater....untill someone noticed the dimmer switch was on fire!
You'd just love to have seen that.
I went to quote on a new job the other week. TT caravan and outbuildings. Asked to see the origin/cut-out and he opens the cupboard. We both stand there watching the upfront 30mA RCD (yeah I know) smoking. All I could think was to turn to the customer and ask if it normally did that! I just wanted to get photos but isolated the power etc :)
So, 1970 ish flat, 16ed board fitted in 2007, MCB covering lighting circuit. Lighting circuit has 4 x 2A/5A sockets on it.
Should they be covered by RCD/RCBO?
My feeling is no and code it C3, with a recommendation to upgrade MCB to RCBO?
Thoughts please chaps.
No code for me, this coding has become total bollox
Not coding isn't an option. Lack of RCDs for additional protection is supposed to attract at a minimum a C3 coding (see notes appended to Electrical Installation Condition Report).
Lighting circuit with 2A & 5A sockets
Octopus,
Octopus,