Discuss Garage Supply - 2 way metal consumer unit in a seperate garage in the UK Electrical Forum area at ElectriciansForums.net

Dunc88

-
Reaction score
4
Hi,
I'm installing a 2 way metal consumer unit in a seperate garage, the earthing arrangement in the property is TNCS. I am planning to install a new 4mm2 ciruit from the main consumer unit in the house, in 4mm2 swa to a garage consumer unit (5M run of cable).
There are no extraneous-conductive parts in the garage, so can I gland this swa directly into the garage consumer unit and have an RCD main switch feeding 1x 16a & 1x6a mcb? If so, how do I prevent both RCD's tripping (garage & main consumer unit)?
Would RCBO's still trip the RCD back in the main consumer unit?
Could I turn the garage into its own TT system? I could gland the swa into an adaptable box next to the garage consumer unit, & join the earth from the 4mm core to the swa inside that box, carrying the Live & Neutral through into the garage consumer unit, from there I would take a seperate earth down to an earth spike.
Thoughts/advice please!
Cheers
 
as long as the feed cable from the house CU does not require RCD protection ( i.e. SWA and/or internal feed in house not subject to 522.6.101 then MCB the feed at the house CU. I'd up the cable to 3 core 6mm on a 40A MCB ... 1. to get a bit of discrimination. 2. to allow for increase in load in the future. then tere's only 1 RCD to worry about. and exten the TNC-S to the garage.
 
Assuming the board has non rcd ways.
Thanks for the feedback all! Unfortunately not, no space for an rcbo! Its fed via an mcb on a split load board. It also starts as 4mm twin & earth before entering a weatherproof box (where i'm glanding the swa in), so from there could I not just enter the garage consumer unit and gland the cable straight in? Then just have a main switch as the circuit from the main consumer unit is protected by the rcd?
 
as long as the feed cable from the house CU does not require RCD protection ( i.e. SWA and/or internal feed in house not subject to 522.6.101 then MCB the feed at the house CU. I'd up the cable to 3 core 6mm on a 40A MCB ... 1. to get a bit of discrimination. 2. to allow for increase in load in the future. then tere's only 1 RCD to worry about. and exten the TNC-S to the garage.
I like this idea, would mean altering the work i've already done slightly, id have to remove the small peice of 4mm twin & earth, & raise the height of the adaptable box on the external wall so i can just run the cable straight into the back of the consumer unit once its glanded in... would mean the main consumer units rcd would trip but at least theres no RCD's in series?
 
Why do you need an RCBO for the swa?
What do you mean by 'have a main switch'?
 
I like this idea, would mean altering the work i've already done slightly, id have to remove the small peice of 4mm twin & earth, & raise the height of the adaptable box on the external wall so i can just run the cable straight into the back of the consumer unit once its glanded in... would mean the main consumer units rcd would trip but at least theres no RCD's in series?

Why would the main rcd in the house trip? The rcd protection would be in the garage. I think I'm missing something here.
 
He has a Rcd protected supply to the garage
He can have a isolator as the main switch in the garage
Pointless TT ing and Rdc ing the garage end if its fed from a household Rcd,it would be a ---- up which pops first

Is ---- as in coin a swear word :)
 
But as per telectrix why doesn't he feed from an mcb in the house - he's using armoured so no rcd protection needed.

Yes fully agree with not tt'ing.
 
Well Dunc,It seems to be going round in circles in this thread
The 64K dollar question,can you feed it from a non Rcd protected mcb or no :)

Add
How has the twin and earth feed to the adaptable box been wired
 
But as per telectrix why doesn't he feed from an mcb in the house - he's using armoured so no rcd protection needed.

Yes fully agree with not tt'ing.

I've got 14 ways at the main consumer unit, all of which are protected by the 2x rcds (7 & 7), so the 4mm comes from one of those mcbs, I was just hoping to avoid it tripping at the house (& knocking off other circuits) but because there is no space for an rcbo/none rcd protected mcb it looks like i'm going to have to just use a main switch & mcb's in the garage and deal with it if a fault does ever occur. To be honest i'm only having a few twin sockets & a couple of lights, just being over cautious!
 
Well Dunc,It seems to be going round in circles in this thread
The 64K dollar question,can you feed it from a non Rcd protected mcb or no :)

Add
How has the twin and earth feed to the adaptable box been wired

Tricky one isnt it!
I took a 4mm t&e from the mcb and buried it in the wall before drilling it and feeding it directly into the back of the adaptable box on the external wall...
 
time delayed rcd in the house protecting the garage circuit, that way the rcd in the garage consumer unit will trip first.

The op has already said the cu is a dual RCD unit with no spare ways - how is adding a time delay going to improve the situation? And why do people think by TTing a shed or garage would prevent the house cu RCD tripping?
 
Replace one rcd with the delay one? OP wants to avoid the garage potentially tripping an rcd in the house, so if there's a short in the garage the garage cons unit should trip before the house one if it's a timer delay one. On a 5m run it's not that big a deal to have to flick a switch in the house c.u. We recently did a farm shed that was about 120m from the main supply and that's what we did - time delayed rcd in house c.u. and normal rcd in the shed. 16mm cable to run the power to the shed because of the length of run with voltage drop.
 
Shame it's not a high integrity dual rcd board, I just installed a similar set-up, but used an mcb to protect the 4mm swa for the garage which had a 63A RCD main switch with 2 mcbs in the unit.
Never been a fan of large consumer units with no none RCD ways.
 
Replace one rcd with the delay one? OP wants to avoid the garage potentially tripping an rcd in the house, so if there's a short in the garage the garage cons unit should trip before the house one if it's a timer delay one. On a 5m run it's not that big a deal to have to flick a switch in the house c.u. We recently did a farm shed that was about 120m from the main supply and that's what we did - time delayed rcd in house c.u. and normal rcd in the shed. 16mm cable to run the power to the shed because of the length of run with voltage drop.
Because it would make the other existing circuits non compliant
 
The only thing that's not been mentioned and I'm sure someone will correct me, I was told by an ELECSA assesor that you're not allowed to export a TNCS earth in less than 10mm cable. So, as you can't get an mcb unprotected in the house consumer unit, have a main switch in your garage consumer unit and put an earth rod in to earth your garage consumer unit.
 
The only thing that's not been mentioned and I'm sure someone will correct me, I was told by an ELECSA assesor that you're not allowed to export a TNCS earth in less than 10mm cable. So, as you can't get an mcb unprotected in the house consumer unit, have a main switch in your garage consumer unit and put an earth rod in to earth your garage consumer unit.

Here goes then; in a typical domestic property, the 10mm bit only relates to the minimum size cable if you have extraneous conductive parts to bond. Or run a separate 10mm protective bonding conductor to the extraneous conductive part in the garage, and run an appropriate sized swa for load/vd only. Or as you suggested turn supply into TT, bonding locally as necessary.

Don't think there is an extraneous conductive part in the situation described by the OP.
 

Reply to Garage Supply - 2 way metal consumer unit in a seperate garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
889
Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Replies
30
Views
583
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
804
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock