Discuss Has anyone seen a service head like this before? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello guys
Just finished an installation for a client and got to the testing and cert phase and thought id check the primary device.
i found an old rewire able fuse holder with what looks to be a copper cable installed as opposed to fuse wire.
Can i get some fuse wire to protect 25mm cable sufficiently as i only have the usual 3036 30a-6a wire?
The "fuse" is NOT something you should be altering or changing.....
What rating is the service head fuse wire?
Why do you need 25mm tails?
The head currently has a copper 2.5 cable and no fuse wire.
I have only installed a new circuit on a DB which has 25mm tails.
I have a habit of checking the service head if the tags have been cut when doing an install cert.
I was hoping to get some 60a fuse wire but your correct I should just tell client to speak to DNO.
On that subject is as simple as client contacting her service provider?
Generally the DNOs won't remove those old fuse carriers live due to the number of accidents which have occurred, and you're doing it with no special training or protection, are you mad or suicidal?
Hello dave
You may have the wrong idea, i was simply talking about the possibility of changing the copper wire you can see to a 60a equivalent fuse wire.
However the advice of overyone has been greatly received and I will get client to get the DNO to change the service head as opposed to me changing the fuse wire. (Which I should not Ben touching anyway)
And yes if I were to even think about changing the service head I would be daft which I would never even dream of even if I were to be paid a million squid
I agree. You need to get the DNO (probably UKPN if u in london) to come and look at that. Tell them its as old as the hills and falling apart.[/QUOTE]
Thanks Taylor
Would mentioning the fuse wire being copper to the DNO be a bad idea as the DNO may come after me for pulling the fuse and just say like you said the service head is ancient?
Just say its really old and looks dangerous. Can they come and check it please.[/QUOTE]
Good shout I am emailing clinet not to make this priority, side point is that we have a 2.5mm copper cable supplying the entire house which must have been like this for some time bloody hell!!!
Good shout I am emailing clinet not to make this priority, side point is that we have a 2.5mm copper cable supplying the entire house which must have been like this for some time bloody hell!!![/QUOTE]
2.5mm bare copper wire is roughly round about, in the same ballpark, approximately, equivalent to a 100A fuse wire, so what's the problem? :mad:
Hello dave
I don't think I do have the wrong idea, most DNOs won't allow their guys to pull the fuse out live due to them being too fragile and too great a risk of arcflash. Pulling the fuse out is exactly what you have done.
You have a really good point and yes thinking about it the head was quite old and if anything happened the only fuse protecting the head would have been at the sub satation
2.5mm bare copper wire is roughly round about, in the same ballpark, approximately, equivalent to a 100A fuse wire, so what's the problem? :mad:[/QUOTE]
Sorry (not) was a rather bad typo, we contacted the supply authority asap and they are coming out tomorrow, long story short I have learnt I should not the check the service head but at the same time I am glad I did because this client is a friend and that was really dangerous.
Last one of those I had to deal with, was buzzing, had steel legs instead of copper.
Had to re-tighten all terminations, file corrosion from the legs and adjust the legs so they made better contact.
Usually check all that before starting an installation, the service head, bonding & tails condition & any N to E surprises.
Hello spark dog, Yes in future I will be doing the above because I don't want this again.
If the head looks old I will say get ukpnw out to check it as it's suspect.
When you say N-E surprises do you mean you check for current flowing down the main earthing conductor or IR check?
the problem with pulling those old service fuses is that the ceramic could break in you hand and give you a lethal shock. even the DNOs are wary.
remember years ago being disturbed while I was doing some testing to find circuits in a very rubbish install & I used bit of 1mm as a link & forgot & put the main fuse back in with link still in place the 1mm copper held up the main 60amp fuse did not.
had replacement head fuse on board. new what I had done immediately removed link re-instated power & finished testing.
that 2.5mm will probably hold as long as it has been in place.
After a staff discussion I am closing the thread on the grounds that what is being shown is illegal and also because we have a lot of trainee electricians on the forum and I don't want them to think that this is an acceptable way to do things.
Reply to Has anyone seen a service head like this before? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Hello, we're looking at relocating the CU fairly urgently for a small business (retail shop) and came across this service head. Obviously need to...
4K