Someone has asked for an upgrade to their consumer unit but they have no water bonding. I explained this and said it needs to be done but it's quite a job and they don't want it done, just the CU upgraded?
What's the crack with that?
Can you crack on and put it down as a departure from bs7671?
Or walk away, safety should have no cost if they wont pay walk away.
So the IET come out with regs, make no attempt to publicise the regs and leaves the poor sparks to educate the public.
This is not acceptable.
So, our responsibility is to make sites safer and, as such, updating a cu to one with. MCB's and RCD's is making the site safer.
Tin hat on
Just saying..
Ps. None of the CPS make any attempt, that I am aware of to educate Joe public either.
My advice to the op is to provide a written quote with the cu and bonding update ... Then see what happens.....
Thanks everyone, just a situation I have not yet come across.
Can anyone give me an example of when you might use the departures section? Just out of interest really. Again, never used it or seen it used!
sometimes you canfind a cold water pipe in an easier location to bond. in that case, it could be noted as a departure, as long as a R2 test confirmed that said bond had an acceptable resistance to the pipe where you'd have liked to bond ( i.e. close to the point of entry ).i done that with the gas here. as the main gas pipe passess next to the CU. the entry point is 10yards away in the attached garage.
Reg 528.3.4
ii) Fault protection shall be afforded in accordance with the requirements of section 411.
If I'm completely off target, please feel free to tell me, I'm here to learn. As far as I'm aware, if you can't guarantee you electrical services, are not in close proximity with other services, section 411 applies?
Reg 528.3.4
Yes but that's nothing to do with main protective bonding of extraneous parts :mtongue::) although it is part of ADS
Chapter 54 deals with protective bonding
Except main protective bonding of extraneous parts is in sec 411. This could go on all night, but suffice to say those with more intelligence than me, have bonded metal internal with plastic service. I'll just follow their lead.
Just seen an ECA survey which states only 6% of businesses surveyed are in full support of the 18th Ed changes, I could have saved them a lot of time and money with that.
thought them wet-pants stopped using lead.
i would say bonding a piece of metal not extraneous could introduce a shock hazard (during fault conditions in the installation) which might never have been there because it wasn't needed such as isolated from earth metal work
i would say bonding a piece of metal not extraneous could introduce a shock hazard which might never have been there because it wasn't needed such as isolated from earth metal work
that's why any metalwork should be tested to determine if it's extraneous. 22kΩ
If you ever read they magazine professional electrician the NICEIC did an article about it but can't remember what month it was.
That's if anyone trusts the NICEIC view :rolleyes:
I realise the OSG is just a guide but it does state in section 4.5 (the green one) that there is no requirement for Main bonding if the incoming service is in plastic.
If there is metal installation within the premises (and plastic incoming) it suggests there should still be Main bonding unless the metal work doesn't test as extraneous.
As an aside, if you don't bond the metal pipe work (after plastic), you'll probably or may have to supplementary bond incoming metal pipes into special locations, perhaps ;)
if the pipework entering the bathroom is not extraneous and all circuits meet their requirement for disconnect times and rcd protected they would be no need to supplementary bond pipes anyway
Protective bonding works with protection a
You type quick, were you poised with a reply :)
Forgetting ancillary earthing, boilers etc. How likely are those pipes effectively be bonded to earth? I would suggest, apart from following like sheep, that's the most cost effective way of following reg 528.3.4 that most installs I've seen, seem to follow?
A measurement can be made to verify the effectiveness of the pipework connected to a main protective bonding conductor
where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition
R =<50 V/Ia in a.c systems
Or
R=<50v/IdeltaN for rcds
Whilst I agree that if the water enters the building in plastic, then it probably doesn't require bonding, however, if the water pipe goes to a boiler, it may then become extraneous if the incoming gas enters in metal. As most boilers use a metal manifold that will ultimately bring the water pipes to the same potential as the gas pipes. The only real way is to test the incoming pipes.
Jay
Jay
Something can't become extraneous just because it's connected to something else that is. It's the gas pipe that introduces the potential, so that's the extraneous part.
Unless you're referring to a situation where the boiler is in an outhouse or similar, in which case each metal pipe that goes to or from the boiler could individually be an ecp where it enters the building.
In a scenario where a plastic water service pipe enters an installation, it is clearly not fit the definition of extraneous conductive part. Similar, the continuation of the service into the property , again in plastic would not be consider extraneous. When a plastic service enters a property, and continues on in metal, then a test could be made to establish if it was extraneous.
However, (I have read and been previously advised) that to conduct that test correctly, all cpc's and other possible parallel paths (like bonded gas pipes to boilers e.g.) would have to be negated, to obtain a true reading, i.e. if those cpc/bonds were removed at a later date. It is also possible, the internal service could be altered, and could be come extraneous.
Which is possibly why I seen very large numbers of plastic services, with their metal internal bonded, or is it a habit out of nature (following like sheep). Its easier to install bonding, rather than retrospectively add it, perhaps. In fact, I have always seen such bonding in place. I note that the OSG recommends bonding of metal services, after plastic, unless it has been confirmed its not introducing earth potential.
However, my previous post was not about main protective bonding, but the application of reg 528.3.4, which will require further reading and seeking guidance. Thoughts?
Sorry Tel, that's 5.
Has the topic lost its flavour on the bed post overnight?
Reply to New CU but no water bonding... in the UK Electrical Forum area at ElectriciansForums.net
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
4K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...