Discuss Removal of extraneous conductive part in the UK Electrical Forum area at ElectriciansForums.net
within a building supplied my a PME system it’s not possible to main bond the extraneous conductive parts effectively back to the origin.
Resolution instead of changing to a TT system remove the extraneous conductive parts.
Water pipe: this comes out the ground so change this to plastic and put a stop cock on the plastic section then box it off.
Soil stack: simply just box it in.
Can anyone see anything wrong with that? Saves allot of agg
Unless I have missed it I assume this relates to your other threads, so is this can install you carried out or an EICR you carried out on an existing installation.
Hi Chris,
This is your 4th thread related to the same issue. Unless there are more I don't know about. You could have kept all the different queries related to it in the one thread.
Just TT the Installation as your assessor has requested.
That's if your customer is now allowing access.
Good luck Pete
P.S. I am now out.
Replaced the fuse board on existing installation, could not access origin at time of install and DNO had no records.
unfortunate for me on my inspection there was access and confirmed PME .
Surely it would be quicker and easier and cheaper to just TT it than bother with changing pipework and carpentry? Would boxing in the soil stack comply anyway?
This was actually a question I was asked in my assessment for stroma and the answer was to TT the installation.....
Reply to Removal of extraneous conductive part in the UK Electrical Forum area at ElectriciansForums.net
During an EICR I have come across a metal tap and copper pipes supplied by a blue plastic pipe. This measures 0.022 MegOhms, this is directly...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
4K
A 'Sunday challenge' for the qualified electricians.... Can anyone explain why a built-in gas meter housing box that is located 600mm above a...
6K
Ok so the scenario is there is an old MICC or pyro 1.5mm 2 core cable supplying the garage run underground on a 16A circuit breaker that is RCD...