Did anyone see it before it was edited?
Did anyone see it before it was edited?
So now your meaning if the voltage should rise the current will increase? I agree but do we really need to consider this in our circuit designs?
Looking at your table if the voltage increased from 240 to 250 the current would increase by less that 2 amps.
just to add, I wouldn't depend on this on a new circuit anyway, maybe like others said I'd consider it replacing a shower.
This is a really good debate, Darkwood has bought up a really good point that I've honestly never thought of in a domestic situation.
Personally I don't think anybody should be using this reg in domestic situations. A shower is a fixed load, same as a water immersion. But along could come Jo blogs and add this on add that on and than a fixed load is a lot larger.
I though will be using this reg to my advantage.
in the airport where I work we see a lot of lighting MCBs tripping out when contactors click over. These circuits serve fixed display stands in shops that never change and nor do the install conditions apsurrounding it.
Where nuisance tripping had occurred on the inrush of florescent tubes even on D16 breakers we than can look at upgrading the breaker to D20/32.
What would happen to your permitted Zs its this that usually limits you from doing this, you still have to meet requirements in the event of a short circuit.
It's exactly as you put it, my Zs would limit me. I could move it from a 16 to a 20 but a you say unless it was 4mm I'd be kinda stuck there, usually these are 4mm because of the volt drop and 16 because of the small load.
Another Possible limitation is if there are any B15,B22,E14,E27 and E40 fittings anywhere on the circuit, as the max OCPD for any of these is 16A.
I edited my last response to you, you be good to get technical tables from your mcb manufacturers as these state the amount of different types of lamps you can have on a given mcb and this is what you have fallen foul off here.
Oh deary me, what appeared at first to be a serious discussion, with self proclaimed superior engineers, then falls apart mid thread with an elementary electrical theory error...and all the abuse 5WWs get!