R

Rajesh Kerai

Recently i have wired a small dwelling house.

I have used 2.5 mm Wire for a radial circuit of 2 double and 2 single sockets. (probably the cable length of 35 m)

I am a bit conscious to know whether it will work for longer time. or i will need to make it a ring circuit.

WHAT DO YOU SUGGEST?
 
as long as it's correctly protected and your Zs and VD values are within limits, no problem.
 
What sized protective device is connected to this circuit? How was the cabling installed? what will be connected into the outlets?

- - - Updated - - -

as long as it's correctly protected and your Zs and VD values are within limits, no problem.
Got to be quick to get in first when your on Tel.
 
If these are the only outlets for the dwelling I would personally run a cable back to the consumer unit from the last socket and put 32a mcb/rcbo in. Once youve plugged kettle in and poss single oven or convector heater for example etc youve a good chance of overloading as it stands.
 
see. that's one problem with creamflow. you don't buy it, you rent it. pi$$ goes in and pi$$ comes out.
 
This Is why I prefer to do 4mm radials compared to rings, you can still have it on a 32a calcs permitting of course, they are easier from a testing point of view and also easier to add extra sockets for the future.
 
I noticed yesterday that hobgoblin is 5.2% in bottles and 4.5% on tap in the pub.....odd.
Funny you say that! I went on a tour of the wychwood brewery for my birthday last week and the reason is that their own pubs were saying that they weren't selling it very well at 5.2% on draught so they done a blind trial at the 4.5% and sold a lot more of it because people weren't getting smashed so quickly and thats how it has stayed!
 
green king is OK. as mentioned previously, hobgoblin is moreish and theakstons old peculier is even nicer.
 
Recently i have wired a small dwelling house.

I have used 2.5 mm Wire for a radial circuit of 2 double and 2 single sockets. (probably the cable length of 35 m)

I am a bit conscious to know whether it will work for longer time. or i will need to make it a ring circuit.

WHAT DO YOU SUGGEST?

So you have already "wired it", and now you are asking us whether it will work for very long?
I'm guessing that this should be in the DIY section.
 
This thread has deviated a bit hasn't it, a good pint of brewers droop might be just the biscuit
 
Well, we've seen it all now. Not only do we have people asking for advice on how to "do electrics" before commencing work, but we have questions after they've already finished. Excellent.
 
.



Back on track ? Thats fair comment,perhaps I can get it back on track with some advise to the forum and the op




=Rajesh Kerai;861066]Recently i have wired a small dwelling house.

I have used 2.5 mm Wire for a radial circuit of 2 double and 2 single sockets. (probably the cable length of 35 m)

I am a bit conscious to know whether it will work for longer time. or i will need to make it a ring circuit.

WHAT DO YOU SUGGEST?[/QUOTE]





After 30 something replies to a very suspect post

I suggest, stop throwing in cables,making them live and generally playing with electrics,it can be dangerous
 
radials have their place. why use twice the amount of cable to install a ring that's only ever going to carry < 20A?
 
If I got a fiver for every radial, I have had to convert into a ring, due to lack of good circuit design it's been loads of money!!.
 
Last edited:

Reply to Radial Circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
325
Hi! Is there any way to know if I have a ring or a radial circuit in a division of the house? Thanks!
Replies
6
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
682
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock