Hoping someone can give me some advice.
My cyclinder immersion thermostat is tripping every few days.
It hasn't been used for a few years, but now, because I got Solar panels and an Eddi connected, we've started using it again.
I've established that the Eddi, nor the top thermostat, is faulty. Both have been replaced, and the problem persists.
The problem is that the thermostat keeps tripping, and when I press the reset button, it works again. But a few days later, it trips.
Could you bottom element be at fault? Could it somehow be the wiring in the system? Any other potential areas to consider?
Any questions welcome. A pic attached.
Many thanks.
 

Attachments

  • PXL_20220304_171555290.jpg
    PXL_20220304_171555290.jpg
    231 KB · Views: 24
The top safety thermostat is tripping it's because it's detecting over temperature in the cylinder or it's faulty and falsely detecting over temperature.

If there is another immersion heater below it then the temperature setting on that one may be set too high causing the top of the cylinder to overheat and trip the top over temp safety themostat.

Is the water from the cylinder very hot?
And is the bottom thermostat turned up high the same as the top one (in the picture), if so that's the problem (or the bottom stat is faulty)?
 
  • Like
Reactions: GarethW
The top safety thermostat is tripping it's because it's detecting over temperature in the cylinder or it's faulty and falsely detecting over temperature.

If there is another immersion heater below it then the temperature setting on that one may be set too high causing the top of the cylinder to overheat and trip the top over temp safety themostat.

Is the water from the cylinder very hot?
And is the bottom thermostat turned up high the same as the top one (in the picture), if so that's the problem (or the bottom stat is faulty)?
Thank you for the reply.

The water in the cylinder is typically very hot, yes. Not boiling by any means, but very hot.

I don't see a temperature adjustment on the bottom thermostat. Should there be one? Pic attached.

Can I just lower the stat in the top? I see there are two temp controls at the top. One with the red switch, and the other has 1-5. Which one (or both) should I lower a little?)

Thanks.

Thanks.
 

Attachments

  • PXL_20220304_171552011.jpg
    PXL_20220304_171552011.jpg
    205.7 KB · Views: 20
lower it a little and see if the problem persists.
 
i would lower both by 1 mark and see if it fixes the problem.
 
  • Agree
  • Like
Reactions: Timbo and GarethW
Presuming the
The red dial? Or the number 1-5?
I presume the Unival is the safety stat?, if so I would leave that at 5 and assuming the adjusting screw above it (set to 4) is the control stat, when the water is very hot but hasn't tripped the safety stat, turn the "4" adjustment screw down until you hear the control stat clicking off, turning the safety adjustment down should test the safety stat setting?.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Cylinder Immersion Heater Tripping
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
GarethW,
Last reply from
johntheo,
Replies
6
Views
5,367

Advert