We have a new Hotpoint oven to install SI4 854 PIX. Old oven was 2.8kW Neff hard wired into dedicated circuit with its own breaker switch on wall. However, new oven, with pyrolytic cleaner, is 3.65 kW, rated but comes with 13Amp plug and lighter gauge wiring. I was going to plug in myself but clearly I need a sparky to convert hard wired socket to plug socket. However, in any case, this seems wrong - surely this requires 16A fuse and heavier duty wiring?
 
33672D9C-27D9-41D4-AD90-43D1754932F8.jpeg
Data sheet says max current 13A. Where did the 3.65kW come from?
 
  • Agree
Reactions: Pete999 and Spoon
We have a new Hotpoint oven to install SI4 854 PIX. Old oven was 2.8kW Neff hard wired into dedicated circuit with its own breaker switch on wall. However, new oven, with pyrolytic cleaner, is 3.65 kW, rated but comes with 13Amp plug and lighter gauge wiring. I was going to plug in myself but clearly I need a sparky to convert hard wired socket to plug socket. However, in any case, this seems wrong - surely this requires 16A fuse and heavier duty wiring?
The 13 Amp fuse is there to protect the cable not the cooker circuit.
Your cooker/oven should have a breaker in the CU.
 
We have a new Hotpoint oven to install SI4 854 PIX. Old oven was 2.8kW Neff hard wired into dedicated circuit with its own breaker switch on wall. However, new oven, with pyrolytic cleaner, is 3.65 kW, rated but comes with 13Amp plug and lighter gauge wiring. I was going to plug in myself but clearly I need a sparky to convert hard wired socket to plug socket. However, in any case, this seems wrong - surely this requires 16A fuse and heavier duty wiring?[/QUOT
When i say cable ,i mean the cooker cable.
 
As @LeeH has pointed out. I can't find 3.65kW in any of the specs.
 
  • Agree
Reactions: Pete999
It may well be 3.65kW total. This usually consists of a fan element and a grill element, which cannot be used at the the same time, hence the 13A rating.
 
  • Agree
Reactions: telectrix
As @LeeH has pointed out. I can't find 3.65kW in any of the specs.

I suspect that figure comes from the rating label on the appliance. Seems all these manufactures don't want to get involved in the cabling for these appliances 'if in doubt, speak to a qualified electrician'!

All instructions now days seem to be obviously vague.
 
View attachment 41256 Data sheet says max current 13A. Where did the 3.65kW come from?
3.65kW is on label on packaging and also on sticker inside oven.

I have meanwhile phoned Hotpoint and although the support phone people were agreeable they knew nothing. They did however contact their tech people who replied, as another forum response indicated, that 3.65 kW is total load from all oven functions, but since this is an impossible scenario 3.65kW is never drawn at ay one time, and so 13A is fine. So seems all ok. BUT, I have to wonder ... what's the purpose of the 3.65kW rating? Surely a max possible kW would be more useful?

Thanks anyways guys. Will get a pro to convert to plug socket for me :)
 
3.65kW is on label on packaging and also on sticker inside oven.

I have meanwhile phoned Hotpoint and although the support phone people were agreeable they knew nothing. They did however contact their tech people who replied, as another forum response indicated, that 3.65 kW is total load from all oven functions, but since this is an impossible scenario 3.65kW is never drawn at ay one time, and so 13A is fine. So seems all ok. BUT, I have to wonder ... what's the purpose of the 3.65kW rating? Surely a max possible kW would be more useful?

Thanks anyways guys. Will get a pro to convert to plug socket for me :)
Think you may have been fobbed off
 
The Rating plate should indicate what the power of the cooker is, to say it was on the packing, may be true, but the plate should have indicated that as well.
 
The Rating plate should indicate what the power of the cooker is, to say it was on the packing, may be true, but the plate should have indicated that as well.

Think that's what the OP is referring to, when he mentions 'sticker inside the oven'?
 
convert the cooker outlet to a BS1363 socket. plug it in, switch on as much as you can ( on the oven ) and clamp the line cable off the MCB. (and see if the plug top gets hot. :eek:).
 
3.65kW is on label on packaging and also on sticker inside oven.

I have meanwhile phoned Hotpoint and although the support phone people were agreeable they knew nothing. They did however contact their tech people who replied, as another forum response indicated, that 3.65 kW is total load from all oven functions, but since this is an impossible scenario 3.65kW is never drawn at ay one time, and so 13A is fine. So seems all ok. BUT, I have to wonder ... what's the purpose of the 3.65kW rating? Surely a max possible kW would be more useful?

Thanks anyways guys. Will get a pro to convert to plug socket for me :)

I suspect, I might be wrong, that CE or EU or Brexit regulations require total load of an appliance, you've probably chucked out the numerous energy level/product data sheets and other completely useless documents that accompany appliances, such as these. In your case, as Andy stated, you can't turn everything at the same time. My old range cooker, had a lower rating, managed on a bit of 1.5mm flex and took 12hrs to cook the Sunday Roast.
 
Why have I been fobbed off?

See you've been two timing us with another forum :rolleyes:

Think that's all you'll get from a manufacturer, not bad advice?

I might be minded to do what Murdoch suggested, if the manufacturers allows, cut off plug & connect to the existing cooker outlet.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
13A plug on a new 3.65 kW oven?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
Paul Wenman,
Last reply from
Midwest,
Replies
19
Views
22,651

Advert