SteveC

I am converting an outbuilding into an office. There will be a few lights, and a few 13A sockets on a ring main for supplying a kettle, microwave, radio etc. Occasionally, outdoor equipment such as a lawnmower or drill may be plugged into one of these sockets for short periods.

So far so good. However there will also be a second ring main, feeding an IT system (several computers, printers scanner etc). This will be run in PVC maxi trunking which will also incorporate the 13A sockets (and probably one or two network sockets). I could meet 17th edition requirements by having this IT ring main protected by an RCBO or RCCB (separate from the one protecting the other stuff). However I am nervous about supply reliability. I understand that sockets feeding computer equipment can be excluded from the requirement to protect by RCCB/RCBO. In that case I would just feed the IT system ring use a simple MCB in the consumer unit. Is this correct and, if so, what, if anything would I need to provide in the way of notices labels etc?

Or am I being too paranoid? Should I just go with an RCBO or second RCCB?
 
What do you mean by being nervous on supply reliability, nuisance tripping?

Its all down to the load you intend the ring final to withstand at the end of the day.

Take a look at Reg 411.6, and table 41.1 (As these disconnection times still apply to IT systems)

Seems that if a continuous supply is required to the system then you need to look at installing IMD's &/or RCM's. I think its heavily circumstantial as to your clients requirements!

Alex
 
You should be ok with up to six or so computors on the same ring
You can also connect the ring cpcs to form the functional and protective earthing
You could perhaps fit non standard sockets for the computors and forget the rcd for the dedicated circuit
 
IT suites should have a 4mm (singles) earth cable, run in a ring round the sockets, using both earth terminals on the back of the socket. This is due to high earth leakage current.
Have worked on similar jobs/installations.
 
IT suites should have a 4mm (singles) earth cable, run in a ring round the sockets, using both earth terminals on the back of the socket. This is due to high earth leakage current.
Have worked on similar jobs/installations.


For a 2.5mm twin and earth ring main
The cpc of the circuit can act as both the functional and protective conductors
The total size of the conductors is less than 10mm which is the requirement when installation of a seperate functional earth conductor
The ring cpcs need to be connected to their own individual terminals at sockets and also at the consumer unit
 
For a 2.5mm twin and earth ring main
The cpc of the circuit can act as both the functional and protective conductors
The total size of the conductors is less than 10mm which is the requirement when installation of a seperate functional earth conductor
The ring cpcs need to be connected to their own individual terminals at sockets and also at the consumer unit

i would put Uninterruptible power supply (UPS) in a IT room as well with earth tags to each ups so it if does trip the computers or server will still be online but monitors will be off UPS have mains filter in as well and warnings of spikes,jumps and mains noise
hope this helps as well with all the other info on cpc & bonding to backplate/sockets
 

Reply to 17th Edition and Computer Equipment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
218
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
I am sure when I qualified for the 16 edition we spoke about how to treat a ring main. I know the majority of the time we just learned how to read...
Replies
178
Views
14K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock